I'm working on the demolition plan for a concrete ramp at a parking garage.
We have the plans for the original building (no ramp) that was constructed around 1940. We have the rehab/modification plans (still no ramp) that are dated around 1980.
Existing plans for the ramp are NOT available. Probably constructed sometime in the 1990's.
Curve radius is about 45-ft at the ramp center. No visibly exposed post-tensioning caps.
Would a curve that tight be post-tensioned along the curve?
Thanks for the input!
Photo of underside...
Link
We have the plans for the original building (no ramp) that was constructed around 1940. We have the rehab/modification plans (still no ramp) that are dated around 1980.
Existing plans for the ramp are NOT available. Probably constructed sometime in the 1990's.
Curve radius is about 45-ft at the ramp center. No visibly exposed post-tensioning caps.
Would a curve that tight be post-tensioned along the curve?
Thanks for the input!
Photo of underside...
Link
RE: Demolition of Curved Parking Garage Ramp
Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?
-Dik
RE: Demolition of Curved Parking Garage Ramp
RE: Demolition of Curved Parking Garage Ramp
Could be done with PT, but would require careful location of dead and live anchors.
RE: Demolition of Curved Parking Garage Ramp
Second, I agree with others that PT pockets should be visible somewhere at the perimeter or in-between sections. If you cannot see them, I would think it very unlikely to be PT'd. Ingenuity has more experience as a restoration contractor with PT'd decks though so hopefully he will comment.
Lastly, agree with dik that scanning would be a must prior to confirming any plan. If even for electrical or something running in the beam (I've seen major ducts run in-between slab expansion joints so that is not as crazy as it sounds). I use xRadar in Ontario as I have found them to be far more accurate than other GPR companies.
RE: Demolition of Curved Parking Garage Ramp
Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?
-Dik
RE: Demolition of Curved Parking Garage Ramp
When it comes to GPR scanning to detect (or not) PT - not all technician (nor equipment) are created equal.
Last week I got called to a commercial kitchen re-model where the GC was to install new floor sinks. They called a scanning company and told them it was a PT slab. GRP detected a 'target' at mid depth of a 7-1/2" slab - clearly labelled it as REBAR and GC had EoR approval to cut one rebar, so GC cored a 12" dia hole. It was a PT tendon. A rebar at mid-depth is not common - should have been a red-flag that it was a possible tendon. Two-way banded/distributed PT slab BUT with added 'no-drape' P/A tendons parallel and between the banded tendons - which is also unusual for North America.
Makes for an expensive floor sink.
So carefully select your GPR scanning company.
RE: Demolition of Curved Parking Garage Ramp
Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?
-Dik