DG Step-Up Transformer Winding Configuration

DG Step-Up Transformer Winding Configuration

DG Step-Up Transformer Winding Configuration

(OP)
I need some comments and/or standards to refer to regarding wye-delta choices for a step-up transformer for diesel generators.
I have (3) 1.5 MW DG Units (with a resistor ground) generating at 4160V. We need to get this connected to the 12.47kV grid, so we will install a step-up transformer (5MVA) to do this. Do I choose Wye grounded or Delta for the Generator side of the new transformer? The 12.47kV winding will be wye-grounded. Thanks.

RE: DG Step-Up Transformer Winding Configuration

The best, for the generator, is delta on the generator side.

I’ll see your silver lining and raise you two black clouds. - Protection Operations

RE: DG Step-Up Transformer Winding Configuration

David,
How is this best for the generator? The grounded wye-delta will provide a ground source on the 12.47kV system, possibly compromising protection.

See IEEE 1547.2.

RE: DG Step-Up Transformer Winding Configuration

(OP)
Thanks for your comment. Is delta better due to no line-ground fault levels at the genset, or are there voltage stability (or harmonics) consideration in having a delta?
These gensets were installed in the 80's and were connected directly to our 4160V wye system.

RE: DG Step-Up Transformer Winding Configuration

(OP)
I can accommodate for the grounded wye 12.47kV on the transformer. I'm also interested in making sure that I can run these units islanded and push a limited amount of MW out to the 12.47kV grid if needed.

RE: DG Step-Up Transformer Winding Configuration

Delta suppresses (provides a closed path) triplens and maintains balanced voltages.

RE: DG Step-Up Transformer Winding Configuration

The delta facing the generator as David suggests better distributes unbalanced loads on the generator.
Consider a delta/wye with a single phase load line to neutral on the wye side.
That will become a line to line load on the delta.
One generator phase winding will contribute directly to the current and the other two phase windings will contribute an equal amount acting as an open delta.
With a wye/wye connection, the maximum single phase line to neutral load is 1/3 of the generator rating.
With a delta/wye connection, the maximum single phase line to neutral load is 2/3 of the generator rating.
With the current distributed across all three phase, the voltage balance with unbalanced loads is much better as well.

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: DG Step-Up Transformer Winding Configuration

Delta on the generator side.

RE: DG Step-Up Transformer Winding Configuration

(OP)
I really appreciate the comments. The balancing on the loads on the delta will help out. On the existing connection straight to the 4160V wye grid, we've seen a lot of unbalanced load current on the generators. The unbalanced loads on the genset makes it difficult to apply all of the relay elements that I want to use.

RE: DG Step-Up Transformer Winding Configuration

Unbalanced loads cause increased rotor heating. This may eventually lead to rotor failure. The increased heating is less with a delta connection facing the generator.

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: DG Step-Up Transformer Winding Configuration

Since you are going to be an IPP (Independent Power Producer) to export power to grid,
when your gen or generators are sync to the 12.47kV grid, the 12.47kV system should still be
effectively grounded. To fulfill that Utility requirement, your step-up transformer shall be
WYE Grounded on 12.47kV side & delta on 4.16kV side.

RE: DG Step-Up Transformer Winding Configuration

You may consider some type of restricted grounding on the delta or at least ground detection.
Differential protection will cover a lot of possible issues.

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close