Short Circuit Current of Standby Generator
5

Short Circuit Current of Standby Generator

Short Circuit Current of Standby Generator

(OP)

How do I determine short circuit current (L-G and L-L-L) of standby generator set, in the 125-750kw range? How long can a set handle or export this current? What happens when it goes beyond 10 seconds? Does the current differ the first few cycles vs the rest of the duration? What happens to the output voltage when a generator is shorted? Does the short circuit power factor change any dynamic?


In so far I'm getting 7.5 times the rated current for a bolted L-G fault not to exceed 5 seconds and 3 times the rated current for a bolted L-L-L fault not to exceed 15 seconds before stator coils exceed 300*C.

I want to make sure down stream circuit breakers clear before the gen set stalls out or becomes damaged.



RE: Short Circuit Current of Standby Generator

Google:
"Sub Transient Reaction."
"Transient Reaction."
"Reaction."
Googling "Generator Reaction" often brings up all three values.

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: Short Circuit Current of Standby Generator

3
Typically most protection engineers I work with ask for the units generator data sheet or decrement curves, I attached a sample one I had open this morning.
That works if you already have a unit, if you are specifying a unit, then many of the manufacturer's sizing softwares will also provide that info.
Just be aware some of the info you are asking for will be affected by the excitation system type, such as PM, SE or AREP. Also most units used to ship with AVR's that had fixed excitation limiters, newer digital AVR's have adjustable excitation limiters that can be adjusted to affect the maximum time the AVR will go full field.

MikeL.

RE: Short Circuit Current of Standby Generator

(OP)
Do you mean reactance? I was hoping something more specific for the common makes Kohler/Cummins/Cat. And the accompanying voltage drop when shorted.

Can AVR excitation time limits be adjusted on off the shelf units? If I am not mistaken modern gens are programmed to drop the field after 10 seconds.

RE: Short Circuit Current of Standby Generator

You should get the GENERATOR DECREMENT CURVE(s) from the gen. manufacturer for
NL, FL, with AVR on MANUAL & AUTO etc. Those standard curves will provide all the info that you are
looking for.

RE: Short Circuit Current of Standby Generator

(OP)
All right.

But- how do I apply them? Is converting a specific short circuit current and its associated output voltage into an ohm value sufficient in determining breaker opening times?

RE: Short Circuit Current of Standby Generator

(OP)
Also, I have a question here. How is a generator capable of outputting 300% current for 10 seconds when the engine is only rated for 100kw output? Does the engine actually output 3x more torque or is there more into this?

RE: Short Circuit Current of Standby Generator

Mbrooke

It is current at a very low power factor, so not many kw in the fault. [a very general response]

RE: Short Circuit Current of Standby Generator

(OP)
Roughly speaking, do you have any idea of the voltage? I ask because in theory a lower voltage means less current flow through the conductors between the genset and fault point.

RE: Short Circuit Current of Standby Generator

(OP)
Those two docs are gold, diamond and silver bowsmile I will read through them, I have a lot to learn and will certainly enjoy it- at first glance very concisely written with the reader in mind.

RE: Short Circuit Current of Standby Generator

(OP)
Alright- those papers have been immensely helpful. It is beginning to make sense, including field forcing.

However, I want to add a bit on top of the knowledge pyramid. Having the decrement curves, how do I obtain the current magnitude and voltage at the generator terminals as I head gradually away from the generator and my conductors become more resistive rather than reactive? For example sizes 6 AWG and declining in physical size resistance dominates.

Also- what happens to the engine? I'm guessing torque required goes up as more real power than reactive power is required to push V through R vs V through X.

RE: Short Circuit Current of Standby Generator

Simplistically you have to model the generator as a voltage source, shunted by the generator internal impedance in series with the line impedance and fault impedance. Generators tend to be fairly reactive (high X/R) and lines more resistive.

The governor will attempt to maintain constant engine speed while the voltage regulator will attempt to maintain voltage at the terminals (assuming this is a single generator). If the generator is supplying significant load pre-fault, the torque may actually go down with a close in (low impedance) fault because the voltage collapses and there is no longer a resistive load taking real power from the machine.

There are entire books and college courses on these topics. It can't really be covered adequately in a forum like this. Get yourself a good introduction to power systems text.

Alan
The engineer's first problem in any design situation is to discover what the problem really is. Unk.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close