Transformer Impedance Reference
2

Transformer Impedance Reference

Transformer Impedance Reference

(OP)
I have seen 3 different ways of displaying transformer impedance(Z%).

1. Z% based on reference temperature.
2. Z% based on temperature rise.
3. Z% based on capacity.

Are there additional ways to display Z%?
What determines which of these is displayed on the transformer nameplate?
Are these values interchangeable? If not, can you convert between the different values?

Thanks!

RE: Transformer Impedance Reference

Per IEEE C57.12.00-2015: The base kVA is the self-cooled rating and the temperature portion states the "impedance shall be referred to the reference temperature defined as 20 degrees C plus the rated average winding rise."

If you are in the IEC part of the world, I think they do things a bit differently.

RE: Transformer Impedance Reference

Z% (actual Ohms)
Z% based on a stated MVA base (which is not necessarily the Txf MVA rating)
IEC based country (Australia). The second is the more common

RE: Transformer Impedance Reference

% of actual ohms? 100%. Not very useful.

In my experience it is based on the lowest rating of a transformer. This is usually the self-cooled rating, but some transformers don't have such a rating. The mobiles I'm familiar with have a single FOA rating.

RE: Transformer Impedance Reference

2
Transformer impedance is generally expressed as % based on the rated KVA of the transformer and a reference temperature. The effect of reference temperature is negligible with Power Transformers as % R is extremely low compared to % X. % impedance= sqrt (square of %R + square of %X) Only R varies as per temperature.
IEEE - Rated KVA = output of TRF; % impedance based on lowest KVA rating ie ONAN rating; reference temp 20 C + average winding rise ( ie 85 or 95 C)
IEC - Rated KVA is the input of transformer; % impedance based on highest rating ie ONAF or OFAF rating; reference temp defacto 75 C; but option is there as per IEEE practice.
Impedance can also be expressed as per unit basis based on % impedance or in ohms referring to voltage side of trf.

RE: Transformer Impedance Reference

Comprehensive reply. Star for you, Sir!

RE: Transformer Impedance Reference

One more interesting point- %R is not ohmic resistance of winding alone; R from stray loss in metal parts inside tank are also added. % R = load loss / rating in KVA x 100. Ohmic resistance of winding will increase with increasing temperature. But stray losses ( may be 10- 40 % of load loss; hence R from it) will decrease with increasing temperatures. So net effect on R due to change in reference temperature is not appreciable.

RE: Transformer Impedance Reference

(OP)
Thank you for the responses. This is making more sense now.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close