Dear all. I have a question. Would you please help me?
In our propane storage tank (T=-44 C, P=4 mbarg), sometimes CH4 enters so it build up in condenser of propane chilling system and flaring is done by operator in order to reduce pressure of chilling compressor discharge.
How can I calculate amount of flaring? Is it possible?
Frankly I don't have any idea!
Replies continue below

Recommended for you

RE: Calculating of proapne losses in refrigerant cycle

There must be more to this question than what is currently stated, because the answer seems so obvious. You need to know how much gas was vented to the flare and the CH4 concentration in that gas. If you don't know both of those two things, then the only other option is to guess.

RE: Calculating of proapne losses in refrigerant cycle

(OP)
Dear don1980
I could not follow you.
I just want to know amount of flaring, don't need CH4 concentration.

The quesrion is: how could I predict or calculate it (knowing CH4 introduced in main tank)

RE: Calculating of proapne losses in refrigerant cycle

As I understand it (correct me if I'm not understanding it right) the operator is manually opening a vent valve to get rid of the methane which accumulates in the condenser because it obviously won't condense. So, the amount of venting is directly a function of the amount of methane that enters the system- none of the methane condenses so it will all be vented to the flare. But, the vent stream will also have a high concentration of propane. So, the amount of gas that's vented to the flare is a function of the amount of methane entering the system and the concentration of the vented stream (the amount of propane that's swept out along with the methane).

RE: Calculating of proapne losses in refrigerant cycle

(OP)
Yes exactly, how can I cal. It?

RE: Calculating of proapne losses in refrigerant cycle

You can get a rough estimate based on a known amount of methane in the condenser feed stream, a calculated propane concentration in the vent stream (based on known T&P in the condenser), and an assumption that the operator doesn't leave the vent valve open any longer than necessary.

RE: Calculating of proapne losses in refrigerant cycle

Have the operators log:
  1. pressure before flaring
  2. pressure after flaring
  3. time of flaring
Characterize the pipe and fittings from the chilling compressor discharge to the flare into a fluid flow problem, then solve for flow.

Good Luck,
Latexman

RE: Calculating of proapne losses in refrigerant cycle

(OP)
Dear Latexman .
Good idea. But the pressure control system is automatic. So the pressure of the vessel wouldn't change.
PV valve open until the vessel pressure does not increase.

RE: Calculating of proapne losses in refrigerant cycle

Then it is easier, constant pressure, constant flow. My advice is still valid. You can calculate the flow rate x the time of flow = mass lost.

Log the data until you see a consistent frequency, then you can have a consistent loss.

This frequency will be consistent with how long it takes the incoming CH4 concentration to build up to the CH4 concentration in the condenser that causes high chilling compressor discharge pressure. To improve the consistency, specify to the operators the exact chilling compressor discharge pressure, not a range, you want them to start flaring. And, if it makes sense, it may not, specify to the operators the exact chilling compressor discharge pressure, not a range, you want them to stop flaring.

Good Luck,
Latexman

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close