Weird Breaker Tripping

Weird Breaker Tripping

Weird Breaker Tripping

(OP)
Hi all,

We have a strange condition wherein, our 600V switchgear power circuit breaker is tripping at no fault condition.

Here is the current case:

The switchgear is a main-tie-main with N.O. bus tie circuit breaker. The breaker is an 1600A K-Line breaker with solid state trip unit. The relay internal trip unit operates a lockout relay which in turn blocks closing of the the NO tie breaker. The tie breaker can be manually operated by close command pushbutton provided either or both incomer breakers are open and there is no lockout relay trip.

Automatic open transition transfer occurs when there is undervoltage or no no voltage at the line side of either incomer circuit breaker and no lockout trip.

Weird condition.

The incomer breaker A trips with no fault...the reason being is that the lockout relay did not operate nor the breaker registers a trip alarm indication. Because of this, the tie breaker can be closed locally/manually.

Is there any experience here for such weird condition? The breaker was replaced with a new one and still behaves the same way.

RE: Weird Breaker Tripping

There is not enough information given Punisher.
Can you post a diagram of your system?
Is this new equipment or is this a condition that has developed on existing equipment.
What has changed?
Is the incoming voltage trending higher or lower than previously?
Has any wiring, relays or other components been changed?
Have any new loads or equipment been added downstream?

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: Weird Breaker Tripping

It could either be intertrip from the upstream breaker to the incomer-A breaker! Intertrip doesn't initiate any protection and also doesn't cause lockout of the breaker.
Other possibility is a fleeting second earth fault in DC system that is causing the trip contact to be shunted owing to its (the second earth fault) location. This kind ghost trips are common in stations where people leave DC system earth faults (first one) unattended.

RE: Weird Breaker Tripping

Or it could be a bad close latch, where it does not trip, but the latch releases.

Not all breaker openings are a trip.

RE: Weird Breaker Tripping

My initial though was the same as cranky108 - bad latch, but the OP says they replaced the breaker. What are the odds of installing a new breaker with the same failure?

-JFPE

RE: Weird Breaker Tripping

Under voltage release that isn’t satisfied when the breaker closes?

I’ll see your silver lining and raise you two black clouds. - Protection Operations

RE: Weird Breaker Tripping

jfpe-anything that can happen, will happen.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close