Generator Short Circuit Current

Generator Short Circuit Current

Generator Short Circuit Current

(OP)
Generator of 400 V 1250 KVA shows Max 3 Phase Short circuit current of 19 KA . In my opinion it is the maximum three phase SKA that Generator can produce obviously can produce higher P-G fault being solid ground.

We have 3 Generators in parallel.

My question and confusion is that when we model it in ETAP software its 3 phase fault contribution on ETAP run when considering fault at Main bus comes out to be more than 19 KA. Is it possible that generator with rated/datasheet mentioned capacity of 19 kA can feed 24-26 kA in any case.

Should we need to tune ETAP modelling to restrict fault current to 19 kA or is it possible that generator can feed fault current more than fault current mentioned on its datasheet

RE: Generator Short Circuit Current

Could be a number of things. ETAP might be displaying a peak figure, depending on the particular method that ETAP is using.
At 24-26kA it doesn't sound like multiple sets involved in the calculation if they're all the same size, but that is also a factor.
Another possible factor is that the 1250kVA is a user selected rating whereas the base for kVA values might be something else, although it'd be a big jump in size to get to 24kA.

EDMS Australia

RE: Generator Short Circuit Current

Make sure you are not comparing symmetrical fault current with asymmetrical current.

RE: Generator Short Circuit Current

19 kA RMS = 26 kA peak.

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close