Controlled fill QC
Controlled fill QC
(OP)
Starting on a new project. A small sugar cane processing plant in sunny Indonesia. We are scheduled to begin earthworks soon. Going to strip the vegetative layer (20 cm) and do a controlled fill with clay up to grade level for the main building. Total height of fill - 1 to 1.5m. I need help with specifying a QC procedure for this from the owner's side. Our spec is 95% MDD, 20cm lifts.
* Is it realistic to do sand cones on every lift? Several samples?
* I am planning to require a minimum size for the sand cone - 200mm cone with 4L jug.
* What is the proper equipment for compacting each lift? I have seen them simply rolling over the incoming fill with a dozer before. Dozer spreads and drives over, spreads and drives over.
* Is it realistic to do sand cones on every lift? Several samples?
* I am planning to require a minimum size for the sand cone - 200mm cone with 4L jug.
* What is the proper equipment for compacting each lift? I have seen them simply rolling over the incoming fill with a dozer before. Dozer spreads and drives over, spreads and drives over.
RE: Controlled fill QC
RE: Controlled fill QC
RE: Controlled fill QC
RE: Controlled fill QC
Well whadayaknow? We are in Semarang, very close to your old stomping ground :) BigH, if you have anyone you would recommend, I'd love a contact. For geotech, we have been going through the local university, but they are not very talkative. Its hard enough to nego and schedule the testing with them as it is. I guess there isn't a shortage of customers.
I was hoping for some pointers. Some dirty contractor tricks to look out for... How likely is it that they'd be willing to accept testing of every lift?
RE: Controlled fill QC
How big is your area? How many m3 is expected to be? I am not familiar with geotech firm there but you might want to try Dr. Paulus Rahardjo of the Catholic University of Bandung. I will contact him and let him know someone may be calling. GIve me a day or two.
First, you need to establish the borrow/fill material. Characterize it by Atterbergs, Standard Proctor, typical in situ moisture content. As GeoEnvGuy says, sheep or pad foot rollers are usually used. A pneumatic roller has also been used. There are also small tag-along type padfoots. Please provide some details - like the fill areal size, anticipated fill layer thickness. In building a dam in Malaysia and using 22 ton vibratory pad foot rollers, we used 300 mm loose lifts. If you would be using a tag-along padfoot, the lift thickness will have to be less - something like 150 mm. For a large area, this will take time given the tag-along's small size.
There are several ways to determine the in situ density - first off, sand cone. In Asia, labour is cheap and it is typically, in my experience, used. You could also do drive tubes - push in or gently tap in a 100 mm thin walled tube - and then get the density from the core taken - nuclear can be used; I personally have less faith in them - they are typically "off" on the moisture content.
I would suggest, especially given the likely quality of the local contractors to do several density tests per layer. In India, the highway requirements are a minimum of 6 tests (seldom is this done on other jobs but it was a government requirement). You would determine the average and ensure that the average was greater than 1.65x the standard deviation plus the unit weight required at 95%. (or whatever you are using) This is to ensure you have uniformity. Again, the number of tests would be determined on the areal extent of the fill layer.
RE: Controlled fill QC
The area to be filled is about 2400 m2, estimated fill depth 1-1.5m, giving a total fill of 2400-3600 m3. The contractor we are talking to right now said he would do that in 3 lifts. Given your info, seems a bit thick. I will check on the roller weight/size they are planning on using.
Definitely planning on the sand cone, radiation is like voodoo magic around here. For a food safety x-ray, the operator has to complete a *month* long training in Jakarta. Oddly, the contractors around here seem to frequently use CBR (California Bearing Ratio) for quantifying fills. I know it is inappropriate, but what is the mechanism why?
RE: Controlled fill QC
A watchful eye is important. During a work effort, they will spread and fill various areas - perhaps simultaneously. Each of these work areas warrant testing, as these work areas are unique. How big is the work area? How consistent are the soils? That will inform a reasonable testing frequency.
How to address your reference density? I mean is there going to be gray and brown soil? Will that be your basis for which MDD to use? Will it all be red clay with varying sand content and plasticity? Hard to eyeball the correct reference density.
My advice? Have in the field a concrete block and a proctor mold. Carry a frying pan (or Speedy moisture tester) and capture your own proctor density. Perform the test at less than optimum water content and walk the field proctor point onto your lab curve. Now you'll know.
If you check your reference density and focus your tests on the specific work area(s), a handful of sand cone tests may be all that you need on a daily basis.
Bear in mind that the sand cone hole is only a few inches deep, so a 0.5m lift will not be properly gauged.
f-d
ípapß gordo ainÆt no madre flaca!
RE: Controlled fill QC
* What is the proper equipment for compacting each lift? I have seen them simply rolling over the incoming fill with a dozer before. Dozer spreads and drives over, spreads and drives over. this depends on the type of soil, but generally one pass with a dozer is not adequate. you might consider a test fill to determine an approved procedure (type of equipment, necessary moisture conditioning and number of passes/thickness of lifts) and then just forgo most testing after that point as long as they follow the approved procedure.
RE: Controlled fill QC
300 mm lifts give say 5 lift. In lieu of a "trial pad" which would likely not make sense for this site, go with a minimum of 6 single passes of the 22 tonne padfoot. This should give a good result - on the first lift - you can check with the sand cones. For an area of this size, a lift a day would not be unreasonable. Can study the results at night and give okay or not for next morning. Also, observe the behaviour of loaded trucks on the fill that is placed after compaction (when putting on the next lift). Any "sponginess" or rutting? On the material we used in Malaysia (PI of about 20, LL of about 45 to 50), we ran heavy articulated loaded trucks with hardly any deformations under the wheel load (8 passes). When I worked in the area, I doubt there was any such testing on fills like these (road from Semarang to Kudus - 1988).
Spent a lot of time in Kudus - my "home" as we were doing feasibility study for coal-fired power plant - ended up at Tanjung Jati - near Jepara. Played a lot of basketball at the Kudus military base.
RE: Controlled fill QC
f-d
ípapß gordo ainÆt no madre flaca!
RE: Controlled fill QC
fattdad, if I understand correctly, you are suggesting to do the lab proctor curve on the fill sample. Then, say, at the end of the day, do a single-point proctor measurement on-site, followed by some sand cones. Then compare the sand cones against this value? The reason for doing this is to control variability of the fill soil? The shape of the proctor curve would be assumed the same as previously determined in the lab, but it will be transposed onto the nightly single point measurement?
cvg, the project is small in the grand scheme of things. It will be hard to justify a trial pad...
BigH, I like the nightly testing approach. Combined with fattdad's single point proctor, I think that will be my method. The machine will be a 10-ton, vibrating, flat drum in the front. I guess that means I should go with a bit less than 300mm per lift. The fill soil will be large lumps of sandy clay. They call it "tanah padas" around here. I am attaching a picture below. Lab tests will be done shortly. This material comes in boulder-sized chunks (other choice is red dirt "tanah merah", fertile soil that is fine and crumbly, more expensive).
You guys hit the nail right on the head about the standards abroad. I realize that I cannot do things truly 100% properly simply because the techniques/equipment are either non-existent or too expensive, but I still try to get as close as I can with the resources given. In the land of the blind, the one-eyed man is king :)
PS. Kudus KODIM basketball/tennis court is still there and is as popular as ever. I recently played some tennis there :) Where were the other choices for building Tanjung Jati?
RE: Controlled fill QC
My point on the general construction approach - I do not know the level and efficacy of the contractors and you may have one that isn't as well qualified as on "bigger" jobs. I hope I am wrong and that the contractor will do the work according to good practice.
Played many a basketball games a the court. There was a missionary from Erie PA when I was there and every Thursday night he would come from Pati and he and I would pick three girls and play any 5 boys who wanted to try their luck. We usually won - the girls played great when against the boys - but when they played with girls against girls, they were quite sloppy in their play. They were kinda cute - but I was nearly engaged at the time! When I was in Kudus - I stayed at the Asri Jaya until I married, then we stayed for a few months at the Notosari before heading off to Pakistan and then Canada. I really liked the satay ayam we could get at the old stall complex near Simpang Tujuh. Take care - and remember the most important words for a guy when he is with his gal . . . walking down the street or in the mall . . . "Liku-liku laki-laki"!!
RE: Controlled fill QC
Let's say the field point plots below the lab curve. Just translate the lab curve to the new point and get a new MDD. You must translate along the line of optimums (parallel the ZAV).
f-d
ípapß gordo ainÆt no madre flaca!
RE: Controlled fill QC
BigH, pneumatic rollers, you mean like the kind used for laying asphalt? Heh, I like your basketball approach. Did you get a chance to try sate kerbau or tahu telur (some more Kudus favorites)?
RE: Controlled fill QC
CEEN 341 - Lecture 6
In the video, he mentions that the compacting spec is, say, 95% modified proctor, +-3% moisture of optimal.
Question: how does one control the moisture? Spray the area with water? Compact more/less such that the proctor peak is in the right location? What if the soil dries out in the sun afterwards?
RE: Controlled fill QC
Where were the other choices for building Tanjung Jati? One site was near Rembasng - east past the city - beautiful white beach - could wade out 500 m and still have the water just above your waist. The other site was near a rubber plantation west of Semarang.
RE: Controlled fill QC
I think I know this one
RE: Controlled fill QC
There was a provisional ASTM on this topic. My former boss, Steven Poulous drafted it. He was a founder of a US firm, GEI.
f-d
ípapß gordo ainÆt no madre flaca!
RE: Controlled fill QC
Stripped the vegetative layer with a dozer, then 30cm more using dozer + excavator. Placed the borrowed soil elsewhere on the property. Underneath removed material could observe traces of a previous fill with gravelly clay and some natural soft black silt. Proceeded to compact this surface with a vibrating roller (this is the only kind of compactor I was able to source, given the limited supply of heavy equipment).
Just as we were preparing to start the fill... it rained. A lot. The whole field turned to mud. It's been 48 hours since, but still not dry due to cloudy weather.
Question: what is the best way to proceed?
- wait until dry? how dry? to 95% (modified) proctor levels?
- wait until top surface is just dry enough for trucks to pass?
- place the dirt on top of the muddy field as is?
RE: Controlled fill QC
A static sheepsfoot roller would be much better, even one that you can pull around behind a tractor.
You mentioned in your OP that you are required 95% MDD. Which method; standard or modified? Standard is more appropriate for your soil type. Getting 95% MDD with modified will be problematic in that soil.
At this point, I would proofroll the site with a heavy, rubber tired dump truck to find the "soft/pumping" areas and scarify them to allow them to dry quicker. If the whole site is mushy, then scarify or disc the whole site and start over with compaction after drying to about 1 to 1-1/2 percent over optimum. For this type of soil, compaction is easier and more efficient if your compaction takes place at or slightly above optimum moisture as it is drying back. If you wait until it dries to a couple of percent below optimum moisture you'll have a lot more difficulty getting compaction.
RE: Controlled fill QC
RE: Controlled fill QC
RE: Controlled fill QC
@azza....Obviously can't control the weather, you just have to accommodate with procedures. Drainage ditches and pumping are the better ways to handle a larger site. Usually a perimeter drainage swale with a diaphragm pump works well.
Good luck. Wet, clayey sites are tough to work with.
RE: Controlled fill QC
Ron, sigh, indeed. Past two days have been tough. Despite some drying out on the surface, underneath it is still wet in some areas, up to maybe 30cm in the worst spots. The quarry where the fill is coming from is also wet, everything they send is wet. I could reject it all, but then I'd have no soil :( (I'll tell you guys some tales about procuring fill some other time, it's a mess). We're spreading it as thin as we can, but just as you guys said, the smooth roller is not compacting it very well. Changed the fill to one containing more gravel and sand, but it is still too clayey and too wet. All hope is that the weather stays good and this thing dries as we lay it.
I was originally targeting 95% modified, but after some preliminary measurements it does look very tough to reach indeed. Getting 85-ish % in bad spots, 90-ish % in better spots. I will re-build the proctor curve as a regular proctor using the new gravelly soil and set the new target at 95% regular proctor.
RE: Controlled fill QC
I've been detained for 24h just for having a map.
RE: Controlled fill QC
RE: Controlled fill QC
RE: Controlled fill QC
RE: Controlled fill QC