Overpressure Protection of Valve Actuators on Instrument Air Systems

Overpressure Protection of Valve Actuators on Instrument Air Systems

Overpressure Protection of Valve Actuators on Instrument Air Systems

(OP)
Hi all,

My plants instrument air header is designed for 150 psi and operates at around 100 psi. The IA is then typically let down to 50 psi or so by a small regulator when used for valve actuators or pneumatically driven pumps. I assume that if you connect a typical control valve diaphragm actuator like a Fisher 667 to pressure source and slowly increase the pressure, at some pressure it is going to fail i.e. it has a maximum pressure rating. But in googling and reading product datasheets, I do not see the "MAWP" of a diaphragm actuator discussed anywhere.

I'd like to understand why we don't include PSVs on the downstream side of instrument air regulators that feed into things like valve actuators. If I don't know the MAWP of the end device how can I know that it cant be over pressured? I don't think I have ever seen a PSV installed between the letdown regulator and an end device so clearly I am missing something.

Thanks!

RE: Overpressure Protection of Valve Actuators on Instrument Air Systems

Did you look for this ?https://www.emerson.com/documents/automation/instr...

Table 1 gives you maximum pressures no?



I've seen small pressure relief valves between regulators and actuators

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: Overpressure Protection of Valve Actuators on Instrument Air Systems

(OP)
Well shoot, I glossed over that line in Table 1 apparently. I have not seen PSVs between regulators and actuators, but as you can probably tell from my initial question there are many things I have not seen. That gives me enough information to sort out my issue though. Thanks!

RE: Overpressure Protection of Valve Actuators on Instrument Air Systems

If you are considering a PSV, I believe that calls for at least an informal Hazop since you will have to note the change on your P&ID. Your air receiver tank should also be protected with a PSV. The changes should undergo an informal Hazop review.

Do you need the air regulator or can the pressure be reduced? The moment you have a regulator in a pneumatic system you will have to consider:

1) what happens if the regulator fails (open) and;

2) what happens if a technician will try to fix a problem by adjusting the correct set value (provided it was documented anywhere and readible from a reliable gauge)?

Maintaining the regulator costs money as well. Creating too much air pressure costs money. My personal opinion: The best regulator is no regulator.

RE: Overpressure Protection of Valve Actuators on Instrument Air Systems

Why would you NOT run a PSV/s on your IA lines where the supply pressure is higher than the MAWP of any equipment connected to it?
IA will generally serve a number of different processes all requiring different MAWP's so regulators and associated PSVs are really the most economical way to do it.
As bimr mentioned, you will want to size the regulator for full flow of the regulator capacity at fail wide open condition.
Maintenance is a reality (for all equipment), but if you have some form of filtration/conditioning you should many years of reliable service.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now
The Great Project Profitability Debate
A/E firms have a great opportunity to lead the world into the future, but the industry’s greatest asset—real-time data—is sitting wasted in clunky, archaic ERP platforms. Learn how real-time, fully interactive dashboards in a modern ERP allow you to unlock data that will shape the future of the world. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close