Dear Mr BrkfldEE (Electrical)(OP)29 Mar 21 15:31
B. " Will using 2 different taps of a multi-ratio CT work? Will it cause any problems? "
C. I may have mistaken your question. I try to answer as following. e.g. a CT with 200/1 and 100/1 toppings.
1. With present load is < 100A,
a) use 100/1 tapping for any load, depending on the CT Class,
b) at the same time, the 200/1 tap may also be be used for any load, depending on the CT Class; without any problem,
c) when the 200/1 tap is not in use, it SHALL be shorted.
2. With future load >100A but <200A,
a) use 200/1 tapping for any load, depending on the CT Class,
b) the 100/1 tap is not used for any load,
c) when the 100/1 is not in us, it SHALL be shorted.
Che Kuan Yau (Singapore)