Hello, I'm having a doubt about the 50 / 51G protection settings. My system has a transformer (138kV - 6.6kV) with an RGB limited to 400A.
All connections are with CT involving the three phases.
Thinking about a protection between two relays what would be the best way to protect the medium voltage panels.
Is it correct to leave the adjustments according to the attached diagram?

RE: Protection and coordination relay 50 / 51G

I see you have 40A & 0.01s for outgoing feeder and 40A & 0.4s for the incomer. There is ~0.4s coordination margin between the two which is good.

RE: Protection and coordination relay 50 / 51G

(OP)
I understand, thank you.
But that way the circuit was not uncoordinated? because both are with 40A current.

RE: Protection and coordination relay 50 / 51G

It is time based coordination here.
When the fault current exceeds 40A, both the relays (the one in outgoing feeder as well as that in the incomer) will pickup but the incomer relay will not give output and the outgoing feeder relay will trip before that.

RE: Protection and coordination relay 50 / 51G

(OP)
Just one more question.
These are the relay settings as shown in the image.
51G pick-up = 0.4 (40A)
51G time delay = Set time 0.5s
50G pick-up = 0.4 (40A)
50G time delay = Set time 0.01

The 50G protection, should it follow the same thinking as the 51G protection?

RE: Protection and coordination relay 50 / 51G

Quote (Eng.Edward.M)

51G pick-up = 0.4 (40A)
51G time delay = Set time 0.5s
If used, the 51G should have an inverse time characteristic, not a set time. As a definite time element, it is no different than the 50G with a time delay. 51G will never operate if the pickup is the same as the 50G, which has a shorter time.

With an NGR, however, there will be little decrease in fault current with distance, so inverse time elements are not really very useful.

RE: Protection and coordination relay 50 / 51G

Device no. 50 is for protection with no intentional time delay. When we have time delay provision, it should be termed as 50TD. Similarly, 51 is for inverse characteristic. This is from IEEE C37.2.
However, these ae not strictly being implemented with the advent of new devices (electronic/digital/numerical) that come with numerous options.

RE: Protection and coordination relay 50 / 51G

(OP)
Please, would you let me know what is the best way to adjust the 50 / 51G protections?

RE: Protection and coordination relay 50 / 51G

There is no "the best way". There can be many acceptable ways and a vastly larger number of unacceptable ways. Many of the acceptable way may involve balancing different considerations and different protection engineers will find different balance points to be the most acceptable. Different organizations take different approaches, weighing various factors differently. No one right answer, just the universal protection answer of "it depends". But as the last two posters said, 51 is an inverse time element and doesn't have a fixed time delay.

I’ll see your silver lining and raise you two black clouds. - Protection Operations

RE: Protection and coordination relay 50 / 51G

"...best way to adjust.." - that's what is called protection coordination study and it cannot be taught / learnt through a forum like this. Requires a lot of personal effort, unfortunately.

RE: Protection and coordination relay 50 / 51G

(OP)
Thank you all for your help

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close