Modern kitchen electric range

Modern kitchen electric range

Modern kitchen electric range

(OP)
In a modern range, are all of the onboard electronics such as the clock and timers 240 volts? I'm guessing they are such that they don't create a current in the neutral due to the unbalanced load they would create. I ask this question with regard to the chassis shock hazard when connected with a 3 wire plug instead of a 4 wire plug.

RE: Modern kitchen electric range

Not that I know of. I think they're about 50/50 240/120. As far as I also know ranges that stupidly connect the neutral to the chassis are no longer allowed to be sold.

Keith Cress
kcress - http://www.flaminsystems.com

RE: Modern kitchen electric range

Historically, before electronic modulation circuits became common, lower heat settings were achieved by connecting a 240 Volt element across 120 Volts for reduced output.
The current drawn by the clock pales in comparison.

A typical transposition sequence.
Highest setting, = #1.
#1. Two 240 Volt elements fed 240 Volts
#2. The larger 240 Volt element fed 240 Volts.
#3. The smaller 240 Volt element fed 240 Volts.
#4. Two 240 Volts elements fed 120 Volts.
#5. The larger 240 Volt element fed 120 Volts.
#6. The smaller 240 Volt element fed 120 Volts.
#7. two 240 Volt elements in series on 120 Volts.
The more mature fellows will remember the once common 8 position switch controlling electric range elements.
That was 7 heats and off.

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: Modern kitchen electric range

A modern kitchen range uses electricity for the igniters and the clock.

I’ll see your silver lining and raise you two black clouds. - Protection Operations

RE: Modern kitchen electric range

That's a gas. grin

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: Modern kitchen electric range

NEC requires four prong receptacles for new construction, but I believe the three pronged ones are grandfathered. When you buy/install a new electric range or dryer, you'll be asked what sort of receptacle you have so the correct cord is provided.

RE: Modern kitchen electric range

And charged extra for the cord.

RE: Modern kitchen electric range

You could always add a control transformer to run the 120v circuit.

RE: Modern kitchen electric range

It'd be a manufacturers choice and different ones could do it differently. To me, a power supply running off 120V would be "safer" than running it off 240V.

RE: Modern kitchen electric range

Given that there may be several hundreds of Watts being supplied at 120 Volts via the neutral, any unbalance on the neutral caused by a clock may be immaterial.

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: Modern kitchen electric range

Ours had a low voltage system internally, but I never checked if it was 12V or 24V.
Now I use gas ....

= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, consulting work welcomed

RE: Modern kitchen electric range

A bit off topic but I had a co-worker that, in his house, could only watch TV with the electric range turned on. I believe he ended up having an open neutral in the distribution wiring.

RE: Modern kitchen electric range

That was common decades ago when residential mains were fuse protected rather than breaker protected.
This will be a 120/240 Volt circuit.
He has a blown main fuse or an open hot line.
One half of the house circuits work fine on 120 Volts.
The other half of the circuits are dead until the stove is turned on, then light loads will be in series with the stove element and will work.
Many of the heat settings on the stove may not work.
The young and inexperienced want to think an "open neutral".
They are wrong.

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: Modern kitchen electric range

Now THAT is interesting . . . and apropos, as our 1970's vintage 200A residential service is protected by fuses.

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]

RE: Modern kitchen electric range

I was trying to visualize the power flow. I had explained it to him years ago. He did look and found a wire bad been chewed through by a squirrel.

RE: Modern kitchen electric range

An older gentleman that I worked for many years ago told me that in the 40s it was a common issue around X-Mass time.
With all the lights on in a house and the oven and lots of elements going cooking X-Mass dinner, a main fuse would blow.
Many mains were only 60 Amps in the 40s.
In the 50s 70 Amp breaker panels were common for a few years.
By the late 50s 100 Amp breaker panels were common.

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: Modern kitchen electric range

I'm in a rental. We've still got tube and post wiring 🙀 from 1936. Code only requires the kitchen and bathroom be updated in order to rent.

RE: Modern kitchen electric range

Main fuses or breaker?

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: Modern kitchen electric range

Half the house is on breakers half on fuses. I took all of the 3 prong outlets off the fused circuits and put the correct 2 prong back in.

RE: Modern kitchen electric range

GFCIs will give protection on the old circuits as well.
They are a good idea for receptacles where it is not feasible to retrofit a grounding conductor.

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: Modern kitchen electric range

Oh yeah? I'll have to look in to that. I would like 3 prong outlets. Thanks!

RE: Modern kitchen electric range

That's what I did all over my house because it was the old self-igniting steel spiral-wound two-cloth covered "armor" wiring.

The galvanized steel spiral wrap simply heats up if there is a ground fault at an outlet. It can heat the entire spiral up to wall material ignition temperature. Rewiring all the associated outlets to a GFI means that any ground fault gets tripped at the outlet before the spiral can take the short circuit current load and heat up.

Keith Cress
kcress - http://www.flaminsystems.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now
The Great Project Profitability Debate
A/E firms have a great opportunity to lead the world into the future, but the industry’s greatest asset—real-time data—is sitting wasted in clunky, archaic ERP platforms. Learn how real-time, fully interactive dashboards in a modern ERP allow you to unlock data that will shape the future of the world. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close