Hi All,

Is anyone aware of equivalent IEC or other international code/standard that may include the equivalent requirements for working clearances similar to those found in NEC 110.26?

"Throughout space there is energy. Is this energy static or kinetic! If static our hopes are in vain; if kinetic ù and this we know it is, for certain ù then it is a mere question of time when men will succeed in attaching their machinery to the very wheelwork of nature". û Nikola Tesla

RE: NEC 110.26 Working Clearance

(OP)
Thanks for the response FacEngrPE but it appears that neither thread really addresses my questions about the working clearances of electrical equipment below say 1000V or 600V.

"Throughout space there is energy. Is this energy static or kinetic! If static our hopes are in vain; if kinetic ù and this we know it is, for certain ù then it is a mere question of time when men will succeed in attaching their machinery to the very wheelwork of nature". û Nikola Tesla

RE: NEC 110.26 Working Clearance

It has been a while since I needed to work with those standards. Here are some things to try BS:162. extends down to 415V https://electricalnotes.wordpress.com/2011/04/22/m..., but you probably are looking for clearance in front of a panel board.

This document from Siemens https://new.siemens.com/global/en/markets/panel-bu... indicates that the information you are looking for might be in IEC 60204-1, “Electrical equipment of machinery" or IEC 61439. I do not have access to these standards so there is some guessing here.

IEC design is a way to create safe electrical system, but is very different from NEC / NEMA design.

RE: NEC 110.26 Working Clearance

Dear Mr VTer (Electrical)(OP)4 Mar 21 16:31
V. "...Is anyone aware of equivalent IEC or other international code/standard that may include the equivalent requirements for working clearances similar to those found in NEC 110.26?..."
C1. There are German Standard per VDE 0100-Part 729 applicable for < = 1kV as follows:
cubicles with > = IP2X : (Refer IEC definition for IP )
1) between cubicle front to wall; 700mm,
1.1) between protrusion switching handle to wall ; 600mm,
2) between cubicles, cubicle front to front; 700mm,
2.1) between switching handle protrusion between front to front cubicle; 600mm.
C2. Please refer to VDE 0100-Part 729 for full detail.
Che Kuan Yau (Singapore)

RE: NEC 110.26 Working Clearance

I followed up Mr che12345's reference, and found reference to
IEC 60364-7-729 Low-voltage electrical installations - Part 7-729: Requirements for special installations or locations - Operating or maintenance gangways (IEC 60364-7-729:2007, modified); German implementation HD 60364-7-729:2009
in a paper from a German panel board manufacturer Hensel (attached), and then found this discussion
Planning and installation of the low voltage switchgear – The devil is in the detail!
Fred

RE: NEC 110.26 Working Clearance

Dear Mr FacEngrPE (Mechanical)6 Mar 21 17:31
F. "....I followed .., and found reference to ...IEC 60364-7-729 Low-voltage electrical installations - Part 7-729: Requirements for special installations or locations - Operating or maintenance gangways (IEC 60364-7-729:2007, modified); German implementation HD 60364-7-729:2009..."
C1. Thank you very much for the learned advice, pointing out the IEC reference.
C2. I notice in the Hensel document in page 5 " switchgear assemblies must be set up so that the minimum aisle widths are not exceeded. ".
I think it could be a translation error? It "should be?" " switchgear assemblies must be set up so that the minimum aisle widths are not reduced. ". ?. Please advise. Note: English is not my mother tongue.
Che Kuan Yau (Singapore)

RE: NEC 110.26 Working Clearance

English is likely not the first language of the Germans that wrote the Hensel document.
On page 5 I find both of these statements adjacent to the illustration:
Installation site Switchgear assemblies must be set up so that the minimum aisle widths are not exceeded.
Aisle width The aisle width in front of switchgear assemblies with drives, e.g. switches, must be at least 600 mm.

I agree with your opinion the first statement is an incorrect statement, I suspect the German in the original document has an awkward direct translation to English. I think the important point being made is that the handles and other protruding items can not obstruct the minimum isle width.

The other document I cited (the link) has some similar illustrations, and also agrees with your interpretation of the isle way. The second document also makes a point that the OEM may indicate that a minimum clearance is required to service the equipment, and the OEM minimum clearance can be wider then the isle way requirement.

Fred

RE: NEC 110.26 Working Clearance

FacEngrPE (Mechanical)7 Mar 21 03:03
F. " English is likely not the first language of the Germans that wrote the Hensel document.
On page 5 I find both of these statements .....Installation site Switchgear assemblies must be set up so that the minimum aisle widths are not exceeded*. ... Aisle width The aisle width in front of switchgear ...."
I agree with your opinion the first statement* is an incorrect statement, I suspect the German in the original document has an awkward direct translation to English. I think the important point being made is that the handles ...".
.
C. Thank you very much for your learned clarification/advice. Case closed.
Che Kuan Yau (Singapore)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close