Good morning,
If I am interested in overall energy consumption from the heating boilers in a building, is it more advantageous to locate the energy meter in the hot water supply line or the hot water return line?
Simple question but maybe not a simple answer!
Tom
RE: Btu meter location
Surely you want to measure the energy in? Like a gas meter?
Otherwise you will need to know the differential temp or energy if just trying to measure the enrgy use inside the building.
@pedarrin2 is incorrect. A btu meter consists of a flow meter and two temperature sensors, one temp sensor goes on to supply and one on to return. Since both supply and return flow are identical it doesn't matter where you install the btu meter. Just make sure you understand where in your piping distribution you are installing it I.e. don't install the flow meter in the primary piping and the temp sensors in the secondary or vice versa. Also make sure you meet the minimum upstream and downstream requirements of the flow meter.
The btu device is not a field device; it is an algorithm in your PLC or DCS to compute energy consumed
kW = Qx1000x4.2x(t1-t2)/3600
kW = kilowatts,
Q = m3/hr of hot water in circulation
To get cumulative kJ, pass on the kW output of this algorithm to an integrator block; kJ = ∫ kW. dT
Click Here to join Eng-Tips and talk with other members! Already a Member? Login
Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now
Close Box
Join Eng-Tips® Today!
Join Us             Close