How would you handle this combustible concealed space?

How would you handle this combustible concealed space?

How would you handle this combustible concealed space?

(OP)
Combustible construction totally enclosed.

Bleachers in a church.

What has me is the mix between standard upright and interstitial sprinklers.

This is a cross-section and the bleachers are about 80' long so small they are not.

I've dealt with interstitial sprinklers before but nothing with varying heights as shown.



RE: How would you handle this combustible concealed space?

If you look at the tyco CC3, I believe you can have up to 60" of clear space (going from memory), so you could use them throughout. Worst case, put a draft curtain at the split between 60" and 46" area. ≤46" you can use CC3. If you want to use SSU in the 60" area you would be fine.

Travis Mack, SET, CWBSP, RME-G, CFPS
MFP Design, a Ferguson Enterprise
www.mfpdesign.com

RE: How would you handle this combustible concealed space?

(OP)
Travis, whether working with interstitial sprinklers or standard uprights do you see four rows of sprinklers?

RE: How would you handle this combustible concealed space?

I take it the top seat/ boxes do not need sprinklers??

Just from the top of the red line down???

You can't do it with sprinkler at the top against the yellow wall

and the next sprinkler at the back edge of the third row? Right in front of the 3'10" line?

RE: How would you handle this combustible concealed space?

(OP)
The "red lines" are simply dimensions that I added to the architectural drawing..

RE: How would you handle this combustible concealed space?

Quote:

Travis, whether working with interstitial sprinklers or standard uprights do you see four rows of sprinklers?

If it were SSU, i'd do it with 2 and no QR reductions. 18" and 46" level. I would use the fact the vertical change is <36" to avoid all 4. But, the interstitial are a bit more specific. I'd do 4 levels with those sprinklers. You could possibly get one row of SSU at the 46" level and then 2 rows of interstitial at the lower 2 levels. Just need the draft curtain to separate them.

Travis Mack, SET, CWBSP, RME-G, CFPS
MFP Design, a Ferguson Enterprise
www.mfpdesign.com

RE: How would you handle this combustible concealed space?

(OP)
Travis, the only way I can be absolutely correct is to install four rows as shown in the sketch below:



Where the concealed space is <3' I will use interstitial sprinklers and and where >3' then QR upright probably a small orifice.

I have a baffle separating the interstitial sprinklers with the standard uprights.

I know this isn't a big thing but there's four such "bleachers" in the church so if I didn't do it correctly I would be making a mistake four times over.

Oh, and I know I show the heads lower than they should be but you get the idea.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now
The Great Project Profitability Debate
A/E firms have a great opportunity to lead the world into the future, but the industry’s greatest asset—real-time data—is sitting wasted in clunky, archaic ERP platforms. Learn how real-time, fully interactive dashboards in a modern ERP allow you to unlock data that will shape the future of the world. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close