MV/LV Transformer Protection

MV/LV Transformer Protection

MV/LV Transformer Protection

(OP)
Is it standard practice to place inter-trips on the MV and LV breakers when grading across say 1 2MVA tx feeder? - Assuming a single transformer single bus arrangement (no bus couples or parallel tx feeds).

In such a case, my understanding is that the MV breaker should grade with the largest LV outgoing feeder and does not have to grade with the LV incoming feeder (as it doesn't matter which trips first)?

Looking to understand thoughts?

AVR

RE: MV/LV Transformer Protection

Inter trip of LV breaker from HV is standard with all transformer installations when the trip happens to be due to fault in the transformer (that operates transformer protection installed on primary side).
Grading of HV protection with that of LV incomer is not necessary done as it isolates one and the same source.
I know some clients who don't provide any protection in the LV incomer except stand by earth fault protection that operates using LV neutral CT input.

RE: MV/LV Transformer Protection

(OP)
Thanks RRaghunath,

This is what my understanding was too; there is no benefit from this coordination as I can see?.

1) Under this circumstance am I correct in saying that the HV breaker must also protect for a 3 phase short circuit at the LV transformer terminals before the LV incommer (limited by the tx only impedance)?

2) Could Earth fault protection be either provided by
a) the HV Breaker phase protection
b) SEF /REF on the neutral point?



RE: MV/LV Transformer Protection

That's right AVR.
There is bound to be an IDMT Overcurrent protection on transformer primary. That will be coordinated with the outgoing feeders from LLV switchboard and hence may not be fast acting for faults in case of transformer secondary faults, including those in the cables between transformer and the switchgear.
Anyway, transformer is designed to withstand short circuit on its secondary terminals for 2s (IEC 60076).
For earthfaults, neutral CT based earth fault protection works. Of course, this is also coordinated with the LV switchboard outgoing feeders and hence cannot be fast acting. HV phase overcurrent protection will also operate provided the fault yields sufficient current.
If you have REF protection on LV side, that is helpful. But, it may not be standard for LV transformers of this size.

RE: MV/LV Transformer Protection

(OP)
Much appreciated, thanks for your help.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close