Allen Bradley Isolator model 931-TD002 query

Allen Bradley Isolator model 931-TD002 query

Allen Bradley Isolator model 931-TD002 query

(OP)
Hello Support,

I'm on site trying to commission application with several Allan Bradley isolators model 931-TD002. This is a new system not being tested before.
Isolators were installed to isolate/split 4-20mA signal into two outputs.
As per dwg. we are simulating signal directly to isolator terminals 41&42 and for a very short period of time mA signal is present on isolator output and than it goes to "open loop". In order to get it work again need to recycle the power for isolator.
All isolators are same model and have identical behavior.
Could not find detailed manual for this particular isolator. Any suggestions, similar experience.

Thanks a lot

RE: Allen Bradley Isolator model 931-TD002 query

931-TD002 is the publication number.

If you have the basic 931N-C122 splitter, input is on terminals 3 &4, outputs on 1&2 and 5&6. It needs 24VDC power.



If you have the A222, then you get to play with the DIP switches



And if you have the X422, it's designed for bipolar inputs and presumably 4mA in is an elevated output on -20 to +20mA input range.

RE: Allen Bradley Isolator model 931-TD002 query

(OP)
Thanks Danw2 for prompt reply. In fact the model is 931S-U561 and it doesn't have dip switches. See attached photo showing more details.

RE: Allen Bradley Isolator model 931-TD002 query

1. Splitter or not, that is the question.

The 931-U561 is listed as a splitter in the 931 product brochure, but A-B does not use the term 'splitter' like I do.

01

I use the term splitter for one 4-20mA input, two 4-20mA outputs.

But the minimalist description and the product description for 931 universal input modules describes the U561 as having a single 4-20mA output and a discrete digital output. So, yeah, two outputs, but only one is a 4-20mA.

02

03

The product migration bulletin (from the old series to the new series) does not refer to the -U561 as a splitter, but as a single output device.

07

2. Wiring

The -U561 wiring diagram shows
- the 4-20mA input on terminals 11 (+) and 12 (-).
- The single 4-20mA output is on terminals 41 and 42.
- The 4-20mA output is loop powered, so one of those terminals must be +24Vdc from the loop power supply.
- The other output is the digital output on terminals 51/52

06

If you're expecting a 2nd 4-20mA output on terminals 51/52, I think the -U561 is the wrong module.

3. Configuration necessary for a simple isolating repeater?

Configuration for a simple splitter is not necessary, but the -U561 is not a simple splitter.
The product description in one doc (screen shot 03 above) states, "Configure analog and digital output options" and "Configuration via on-board buttons/enocder or FDT/DDTM program".

Another doc with the wiring diagram says the current input is "Configurable".

I'm guessing you probably need the software configuration package (Pactware, a Windows app, the 931 DTM device descriptor file, and the USB/serial converter cable, p-n 931A-CB) in order to tell the box which input it's looking for, what the digital function is, and what the 4-20mA should do in a fault condition. Maybe the 4-20mA action is telling you, "I'm not configured".

04


05

The module might not know which input it's looking for and setting the failsafe fault mode to 'open circuit', which is why the 4-20mA momomentarily appears then disappears.

I tried loading the DTM in Pactware, but when Pactware could not detect the USB/serial cable, it stalled and wouldn't open the device, so there's no way to tell what's next in Pactware.

The instruction sheet for downloading the DTM and installing it in Pactware is attached.



RE: Allen Bradley Isolator model 931-TD002 query

(OP)
Thanks Danw2 for taking time on this.
In the meantime we have also received a confirmation from our vendor saying this isolator/splitter is not correct type for our application i.e wrong parts were installed inside control cabinet.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close