Do the Shear need to be checked in underground precast concrete vault Floor Slabs?

Do the Shear need to be checked in underground precast concrete vault Floor Slabs?

Do the Shear need to be checked in underground precast concrete vault Floor Slabs?

(OP)
I have a question for underground precast structures, specifically rectangular or square boxes, vaults, if I need to check Shear for the floor slab design. I have seen that in several references like Precaster Notebook, a design from Delta Engineering for a CSX Cooper-E80 load and other colleagues, and I checked it always getting thicker slabs, but I found another design example where the Shear was not checked in the floor only in for punching in the top slab.
In other blog here referred to checking shear in concrete slabs somebody commented that : "there is an statement in the Bridge Code saying Shear is not needed to be checked when the slab is designed as a two-way slab" , or did he mean for Top slabs only??

Is this the reference mentioned there?:

"18.4.9 Shear Check of Slab
Slab bridges designed for dead load and (HL-93) live load moments in conformance with LRFD
[4.6.2.3] may be considered satisfactory in shear LRFD [5.12.2.1]." from WisDOT Bridge Manual.

I would appreciate your advice and comments. Thanks.

RE: Do the Shear need to be checked in underground precast concrete vault Floor Slabs?

(OP)
Just to clarify what was said in other post: " slabs designed for moment do not need to be checked for shear"

RE: Do the Shear need to be checked in underground precast concrete vault Floor Slabs?

I can think of no valid reason why a shear check would not be done.

BA

RE: Do the Shear need to be checked in underground precast concrete vault Floor Slabs?

What rationale could there possibly be for not checking it?

The basis of every single failure is an assumption..

RE: Do the Shear need to be checked in underground precast concrete vault Floor Slabs?

Check the shear using beam theory per 1m strip analysis.

I am not familiar with the US Bridges codes but from my bridge design experience I understand that for this specific load, design with Load Reduction Factor would result in a reinforcement arrangement that would satisfy shear requirements de facto. Do you have this loading condition? (or even a bridge?). Bridge loads are normally amplified to account for dynamic effects, so if you don't have a bridge please don't correlate.

From my (limited) underground structures experience I can tell you that we definitely design underground slabs for shear and it is not uncommon to provide single leg links even in exceptionally thick slabs (2m+) 25m below ground. Of course it always it depends on your loads=depends on soil/groundwater + loads from above.

What kind of structure is this anyway? - just curious

RE: Do the Shear need to be checked in underground precast concrete vault Floor Slabs?

(OP)
The ones in the example that I found without checking Shear are for underground Catch Basin rectangular precast box, with the floor slab designed as two-way slab, and in a County Airport, with 30,000 lb wheel load with 240 psi max. tire pressure. That is why called my attention, because all the other references were for H-20 loading and always checked the Shear on the floor.

RE: Do the Shear need to be checked in underground precast concrete vault Floor Slabs?

(OP)
I have run the Shear check for that example, and is ok, apparently was checked but not reported in the calculations. Thanks for your comments.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close