Toxic Gas Detector Time Delay
Toxic Gas Detector Time Delay
(OP)
Hello Friends,
We have Ethylene Oxide EO toxic gas detectors (GDT)in side plant. These is deluge activation linked to these EO Toxic gas detectors. Once these gas detectors 10 ppm (2 time of STEL) value it will activate Deluge system.
EO detectors have inherent cross sensitivity issue and we are facing false activation of deluge.
Is there any possible solution to avoid this?
We are intended to put time delay for 1 min or 2 min, if 10 PPM Value stay for more than 1 or 2 min then deluge to activate.
or is it safe to raise the GDT Deluge activate value to 50 ppm?
Please share your experience.
We have Ethylene Oxide EO toxic gas detectors (GDT)in side plant. These is deluge activation linked to these EO Toxic gas detectors. Once these gas detectors 10 ppm (2 time of STEL) value it will activate Deluge system.
EO detectors have inherent cross sensitivity issue and we are facing false activation of deluge.
Is there any possible solution to avoid this?
We are intended to put time delay for 1 min or 2 min, if 10 PPM Value stay for more than 1 or 2 min then deluge to activate.
or is it safe to raise the GDT Deluge activate value to 50 ppm?
Please share your experience.
RE: Toxic Gas Detector Time Delay
What is typically used is to employ signals from two or more detectors in order to initiate executive action. This depends on how the detectors are positioned inside your plant and what is their coverage area. If you depend on a single EtO detector in any given area, you cannot use this approach.
There is no such thing as "common sense" - Apollo RCA
RE: Toxic Gas Detector Time Delay
One more issue with the detectors that once they detect a value of 10 or 12 ppm of EtO, it will not go back to original within a min, some time in 90 Sec.
So if we put 1 min time delay for 5 ppm, it still can have activation.
RE: Toxic Gas Detector Time Delay
What are the other physiological effects on humans of EtO at high concentrations from which we can choose a more reasonable level for deluge activation ? What happens at the suggested 50ppmv ?