Control Current Transformer as required by IEC60204-1

Control Current Transformer as required by IEC60204-1

Control Current Transformer as required by IEC60204-1

(OP)
IEC 60204-1 requires a transformer for control circuits:
[i]
9.1.1 Control circuit supply
Where control circuits are supplied from an AC source, transformers having separate windings
shall be used to separate the power supply from the control supply.[/i]

Can anyone help me with the background, the contribution to safety of such a transformer?

I know sometimes usage of a transformer has advantages. For example when there is a high short circuit current or when a machine has only 3 phase supply.
But there are also situations in my opinion it is beter whitout transformer. For example when there are long cables in control current circuits. Or when the supply system has a low short circuit current.
I know also there is an exeption, but in general it is required.

So why is it [u]required[/u] and not just allowed?
Replies continue below

Recommended for you

RE: Control Current Transformer as required by IEC60204-1

The code also allows use of directly connected control supply. See the extract as belo:
9.4.3.1.5 Method d) – Control circuits not fed by a transformer
Control circuits that are not fed by a control transformer or switch mode power supply units
fitted with transformers having separate windings in accordance with IEC 61558-2-16 are only
allowed for machines with a maximum of one motor starter and/or maximum of two control
devices, in accordance with 9.1.1.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close