Seeking "right" formula for heat dissipation.
Wally89
Industrial
IT
Hi, I'm struggling to find a univocal answer to my problem.
I have an electric enclosure, I calculated that when outside is 35°c the inside temperature is 76°C
How do I calculate the necessary air flow to bring the internal temperature down to the ambient one (35°c)?
Thanks in advance.
Mathematically, short of an infinitely fast air flow through the holes Keith mentioned, there will always be a temperature rise, even if it's infinitesimally small. If you've done calculations, then you can use the specific heat of air and determine the amount of air mass-flow to raise the temperature by, say, 1ºC, given your power dissipation.
For example, a 1ºC temperature rise requires a minimum of 173 cubic feet/minute flow with 100W input.
trying to design for no temperature is unrealistic and expensive. Your components should already be rated for at least 70ºC
TTFN (ta ta for now)
I would ignore the temperature you calculated baser on heat transfer and use the energi you need to Remove and the heat capacity of the Air. If Q is the heat generated, V is vol flow of air c is the volume heat capacity of air and t is the max temperature you will allow then V=Q/c/(t-35)