Connection design, anchor plate, AS 4100 max pitch requirements

Connection design, anchor plate, AS 4100 max pitch requirements

Connection design, anchor plate, AS 4100 max pitch requirements

(OP)
Hi,

AS4100 Clause 9.6.3 limits the max pitch spacing of bolts in a connection design to lesser of 15tp or 200mm. I have an anchor plate design with post installed anchors at a pitch (centre to centre spacing) of 430mm. Unfortunately the pitch can not be reduced any closer because this is to avoid critical elements in the existing concrete. What actually governs this maximum pitch requirement the standard is setting? The supplementary doesn't offer much information to help.
What should I do now since the pitch exceeds the standard?


Thanks in advance

RE: Connection design, anchor plate, AS 4100 max pitch requirements

In NZS3404 (and in AS4100 I believe), it states something along the lines that this limitation is to do with bolts too widely spaced not clamping together plies sufficiently. Such that there is an increased chances of corrosion occurring as water and rubbish materials can be sucked into any gap that forms which can accelerate corrosion in this gap. I believe that is the primary consideration.

Now if you had a thick rigid baseplate like 50mm thick this would be less of a concern than a 10mm plate. Apply some judgement.

RE: Connection design, anchor plate, AS 4100 max pitch requirements

(OP)
Thank you for your response Agent666 - that makes sense.
The said anchor plate will be fully encased in concrete, reducing the chance of corrosion occurring.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close