hello,

i have a one story builidng which i am investigating if a cantilevered column system is better than special moment frame. the seismic design category is D.
i guess no requirement for beam column joint. asce7-10 specifies that it must be detailed to fit the requirements of SMRF.
Does this mean i need to detail the reinforcement accordingly while designing the column as ordinary or intermediate frame ?
Thank you

RE: cantilevered column system


Table 12.2-1 Design Coefficients and Factors for Seismic Force-Resisting Systems,G. CANTILEVERED COLUMN SYSTEMS; IMF or OMF is not allowed for SDC D.

Special reinforced concrete moment frames are allowed with height limit of 35 ft.

This means; R=2.5 , Overstrength factor Ω0 =1.25 , Cd = 2.5 and comply with detailing req's specified at 14.2.

RE: cantilevered column system

(OP)
thank you hturkak. So i need to design the column as special column and not only adopt the reinforcemeent arrangement of SMRF ?
the problem i am facing with the SMRF is that the columns are quite big for one story (i am still getting an overstressed joint shear even with column 500x500). Is it common to provide a thicker joint at the top of the column ?

RE: cantilevered column system

(OP)
500x500mm

RE: cantilevered column system

Based on my experience, for single story building, OMF and IMF can still work as I believe its height is less than 35'.
I would still open an option for ordinary cantilever column too.
SMF is definitely a heavy deign for a single story building.
Often, what i usually do is, place cantilever columns and make the base fixed by placing grade beams,
simply because the construction (apparently) process gets tricky as you start using Cantil. Col to OMf, IMF then SMF.

RE: cantilevered column system

Quote (structural87 (Structural)(OP))


.....So i need to design the column as special column and not only adopt the reinforcemeent arrangement of SMRF ?
the problem i am facing with the SMRF is that the columns are quite big for one story (i am still getting an overstressed joint shear even with column 500x500). Is it common to provide a thicker joint at the top of the column ?


I want to remind the definition ; section 11.2 ( CANTILEVERED COLUMN SYSTEM: A seismic force resisting system in which lateral forces are resisted entirely by columns acting as cantilevers from the base.)

Pls look to part G of Table 12.2-1 for the detailing req's 12.2.5.5 and 14.2 . For R.C SMRF, ACI limits the cross-section dimensions ,material quality, area and spacing of reinforcement, location of splices, spacing of transverse reinforcement.

I want to remind also, foundations for cantileverd column systems shall be designed with the overstrength factor , 1.25. and the system shall be checked for redundancy..

Regarding your querry, ( i am still getting an overstressed joint shear even with column 500x500). Is it common to provide a thicker joint at the top of the column ? ) .I could not imagine..The cantilever systems should not have rigidly connected beams at the top..

If you post the system, at least some descriptive sketches, you may get better responses..

RE: cantilevered column system

yes, new shop drawing for columns.

RE: cantilevered column system

structural87,

Don't you have walls that can be utilized/designed to meet requirement for special reinforced concrete walls. Then you can use dual system designation, with the requirement that the special reinforced concrete moment frames shall be capable of resisting 25% of prescribed seismic force.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close