FOUNDATION DESIGN FOR HEAVY MACHINE

FOUNDATION DESIGN FOR HEAVY MACHINE

FOUNDATION DESIGN FOR HEAVY MACHINE

(OP)
Hello everyone,

i have a some questions about machine foundation design.

1- do we have to do analysis for wind and seismic for heavy machine( 90000 lb)
or we have to show that overturning FS >1.5 , so no net uplift( but i m not sure witch chapter to use for heavy machine)
2- for anchor bolt, any way to find necessary length or just trial and error.
some reference advice to make anchor as long as possible

Thank you

RE: FOUNDATION DESIGN FOR HEAVY MACHINE

1. Yes, both cases need to be addressed, but wind might not govern for heavy equipment, and it is not required for enclosed equipment, except the enclosure. Follow ASCE7 procedures on chapters for nonbuilding structures to get anchorage force.
2. Follow ACI318 App. D for anchorage design.

RE: FOUNDATION DESIGN FOR HEAVY MACHINE

(OP)
Thank you for the clarification,

I did use chapter 13 and chapter 15( non building structures) to get the force.
The force from chapter 15 was more conservative.

i m following ACI318 App. D for anchorage design.
is there any rule of thumb for minimum embedment of anchor? our block foundation gonna be deep( around 4' due to weight of the machine (90000 lb)

Thank you

RE: FOUNDATION DESIGN FOR HEAVY MACHINE

If you are intended to use headed anchors, you shall follow App. D to determine the required embedment length to develop the pull out/break out strength required for tension. Or for relatively smaller strength requirement, you may consider using post installed anchors. The manufacture's catalog on its website has all required information.

RE: FOUNDATION DESIGN FOR HEAVY MACHINE

(OP)
Thank you Retired13,

RE: FOUNDATION DESIGN FOR HEAVY MACHINE

You are welcome.

One thing to keep in mind, when design anchor in pedestal type structure, the concrete is usually not sufficient due to the limited cross sectional area, therefore, the vertical rebars are to be utilized to provide resistant force. In such case, you need to extend the anchor to below the full rebar tension development length, and let the failure cone intercept that point.

RE: FOUNDATION DESIGN FOR HEAVY MACHINE

Normally the design of machine foundations has its own code and requires dynamic analysis so that the vibration is controlled by considering the machine, the foundation and the supporting soil all working together.

UK has a simple CP 2012. The German has an excellent DIN 4024 (both Part 1 & 2). The American uses ACI351.

On the holding down bolt the standard practice is to cast the HD bolt with bottom washer and a robust steel grouting tubes so that the top of the HD bolt has some free movement for the machine installation. The tube is grouted finally after the machine has been correctly installed and tightened in line and level first with its own grouted baseplates.

A good practice that I recommend is to follow UK CP 2012 practice to provide a 3D cage because you do need (1) the holding down bolts to dissipate the stresses into the foundation. (2) If your foundation split the you are not bolting the full mass (thereby invalidating your computed participation factor) to vibratory equipment and thereafter there is no cure!

As far as I know the holding down bolts should be supplied by the machine vendor and you may need to cast them with a template to ensure the required accuracies are achieved.

Lastly unless someone points a gun at me I usually specify in the drawing a machine foundation to be cast in one operation without any construction joint but exceptions can be made on certain pedestals.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close