hi all
It will be the first time I use the special moment frame in order to stabilize the building consisting of 2 floors I am working on. I am reading some literature about this topic. One of the questions which comes to my mind:
If there is a possibility to add some walls here and there, will it become a dual system in condition to detail the walls as special structural walls ? If the frame should resist 25% of the lateral force, does the wall have any requirement regarding the percentage of force they must be able to resist ?
Thanks
It will be the first time I use the special moment frame in order to stabilize the building consisting of 2 floors I am working on. I am reading some literature about this topic. One of the questions which comes to my mind:
If there is a possibility to add some walls here and there, will it become a dual system in condition to detail the walls as special structural walls ? If the frame should resist 25% of the lateral force, does the wall have any requirement regarding the percentage of force they must be able to resist ?
Thanks
RE: special moment resisting frame and dual sustems
The requirement for dual system , the moment resisting frame shall carry at least 25% of the lateral load. The wall can be OSW or SSW. Pls look the code Table 12.2-1 Design Coefficients and Factors for Seismic Force-Resisting Systems, DUAL sytems, D and E.
RE: special moment resisting frame and dual sustems
That's right, although the system is meant to work with the walls as the primary lateral system and the moment frames as a backup system of sorts.
There is no requirement for the percentage going to the walls other than it should be in proportion to the stiffness of the walls relative to the stiffness of the other lateral elements employed.
RE: special moment resisting frame and dual sustems
In a moment resiting frame, ignoring the slab out of plane stiffness is totally OK right ? So no need to detail the diaphragm slab correct ?
Assuming another scenario, If beams are omitted, is it still OK in assuming the slab as a membrane ( transferring only in plane forces (tension, compression) ?
Thanks for the help
RE: special moment resisting frame and dual sustems
Yes..the slab could modelled assuming semi-rigid diaphragm and should be modeled using shell elements which are semi-rigid in plane, and the out-of-plane stiffness should be modified to near-zero.
If beams are omitted, the remaining system for the seismic loading will be essentially shear walls . Still one cannot assign response modification factor for RC slabs. Check your local code...some codes allow the use of hidden beams which are ductile detailed for flat slab systems. However, in order to satisfy drift requirements, you will need shearr walls which will be primary seismic load resisting system.
RE: special moment resisting frame and dual sustems
RE: special moment resisting frame and dual sustems
In general, yes. Whether moment frame or shear walls, the diaphragm is performing an important structural function and ought to be designed for the forces induced in it. This is probably even more important than usual in a dual system building because you're passing a lot of forces back and forth between systems via the diaphragm. The one caveat that I'll add to this is for the kind of building where every column in the entire floor plan is part of a moment frame. Diaphragms demands do tend to be quite modest for that kind of buildng.