Dear All Fellows,

Our BFWPH flange is damaged/eaten because of NOx leakage at NA plant. Flange is damaged at 5 locations and max. damaged depth is 25mm.

Repair procedure is developed and attached with post along with respective necessary documents.

Expert opinion is needed for the validation of our Repair Procedure.

Thanks,

 
 https://files.engineering.com/getfile.aspx?folder=c9ee0cb7-26e5-4e16-b184-83bfb7dd20a7&file=Repair_Procedure_for_Damaged_Flange_of_BFWPH-Rev.1.pdf