Longitudinal Reinforcement for Torsion, ACI 318-14, 9.6.4.3 - Units

Longitudinal Reinforcement for Torsion, ACI 318-14, 9.6.4.3 - Units

Longitudinal Reinforcement for Torsion, ACI 318-14, 9.6.4.3 - Units

(OP)
Ref:
1. ACI 318-14, 9.6.4.3, equations (a) & (b)
2. ACI 318-11, 11.5.5.3, equation 11-24

Reference 2 limits the distribution of reinforcement, At/s to a minimum ratio of 25*bw/fyt. The distributed quantity is the area of torsional reinforcement and the spacing of the same. bw is the width of the concrete section (web) and fyt is the yield strength of the reinforcement.

The problem is that the units for the limiting ratio are incompatible with the distributed area. The distributed area results in units of inch. The ratio results in cubic inches per pound, whereas the expected quantity is "inch". (The complete equation has units of area for the final result.)

Reference 1 provides two equations, the minimum area is taken as the lesser of the two equations. It is simply a restatement for that shown in Reference 2.

I do not find any correction in ACI.

What am I missing?
What is the solution?

Thanks.

RE: Longitudinal Reinforcement for Torsion, ACI 318-14, 9.6.4.3 - Units

At/s is in units of (sq. in)/(in.) which, in your result is just inches.

For the limiting ratio (25bw/fyt) the value of 25 has inherent units in it.
Here's an example from PCA (old one based on 318-02) but same equations:

RE: Longitudinal Reinforcement for Torsion, ACI 318-14, 9.6.4.3 - Units

(OP)
JAE:
Thanks for the solution. Your notion of inherent units with the constant '25' is what I missed.
You have made me recall such notions that constants can carry units. dazed But, that was in the days before spreadsheets and worksheets, of which now units are mandatory.
Have a great day.
MGM

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

The Low-Code Digital Transformation Guide
Change the way you develop apps and, in turn, change the way your business operates and engages with customers, leading to new channels of revenue. This ebook is the culmination of 14 years of experience with 4,000 customers that have all transformed their business through low-code development. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close