Column Base Moment Connection

Column Base Moment Connection

Column Base Moment Connection

(OP)
Good day,

I'm working on addition of crane in the existing shop that has 6" slab on grade floor. I will be using cast-in-place piles for crane support columns. One constraint I have is that I don't really have anything to tie into to resist lateral forces caused by crane operation (forces perpendicular to crane runway beams). The only element where I could put some forces is roof diaphragm but I don't want to put much into it.

Making column base connection as moment connection does help but involves many-many anchors. My column base plate will sit below the slab so I was thinking of relying on lateral force resistance by slab working in pair with regular column base connection to produce some moment resistance.

One concern I have is about the rigidity of this slab resistance deteriorating with time after many cycles of loading. I'm basically looking for some feedback on this idea as I'm sure many of you have considered/used this approach before.

Thanks

RE: Column Base Moment Connection

It sounds like you are designing support system for overhead runway crane, and concerned with the lateral thrust produced by the trolley movement. Can you show a building cross section?

RE: Column Base Moment Connection

(OP)


Please let me know if any other info is needed to better understand the situation.

RE: Column Base Moment Connection

Is this a new building addition? Or adding crane only? How much is the lateral thrust you got? How much space is available between the CMU wall and the column, and between the existing and new column in the middle?

RE: Column Base Moment Connection

(OP)
It's adding crane and firewall only. Lateral thrust is 4 kip total (2 per side). I have 3" between left column and firewall and 6" between right column and existing framing.

RE: Column Base Moment Connection

I don't see any reason why the slab couldn't be assumed to provide lateral resistance. As long as the base plate anchorage and edge distance, etc. of the footing are sufficient to resist the shear applied to the base plate.

Rod Smith, P.E., The artist formerly known as HotRod10

RE: Column Base Moment Connection

I suggest to provide CMU/concrete bond beam at the runway beam level, and provide ties that is capable of resisting the 4k lateral thrust. The tie shall consist two pieces, one on wall, and one on column. then connected by bolts through slot holes.

Is there any reason why you can't bring the pile cap to the floor level?

RE: Column Base Moment Connection

Suggest details.

RE: Column Base Moment Connection

Retired: not sure attaching to the cmu creates any better of a load path, but if detailed properly could work.

The slab on grade might be able to be utilized for the lateral resistance but make sure you carry that load path to conclusion and verify enough sliding resistance and capacity. Also need to make it clear that the slab is stabilizing the structure so future work gets coordinated to not remove large portions of the slab.

Open Source Structural Applications: https://github.com/buddyd16/Structural-Engineering

RE: Column Base Moment Connection

It just to take out the lateral load, if the wall is stiff enough, instead of messing with difficult moment connection at the base, yet still produce large deflection at the runway level.

RE: Column Base Moment Connection

I can't quite read the vertical dimension on the left, but it looks like you may have clearance to use a rigid frame, crane columns and a beam above the crane. I would depend neither on the slab or the masonry to provide support laterally.

RE: Column Base Moment Connection

Ideally, it should have a backup truss, but then the wall needs to move farther away, as for now, there is only 3" space between the column and the wall. The wall needs to be reinforced both ways in order to be effective. For 5 ton crane, 4 kips lateral seem a little too high though.

I think the dimension to the roof is 20.5', and wall height approx. 22'.

RE: Column Base Moment Connection

Serhiy2,

Forgot to mention one thing. Before pin down your design, check to see what is the configuration of the bridge end truck wheel - flanged on both sides, or one side. If one side, is on the inner rail side, or outer rail side? The one side type has more tolerance on rail misalignment, but obviously will affect the distribution of lateral thrust, therefore, your design layout.

RE: Column Base Moment Connection

(OP)
retired13,

Thank you for all your input. I was trying to avoid connecting to firewall as it needs break-away connections. Also, there is office mezzanine/2nd floor on the other side of the wall and putting the lateral force in the wall might result in vibrations reaching the office structure. I will check what it would take to be able to use slab on grade to provide base moment resistance.

RE: Column Base Moment Connection

Understand your situation better now. I'll suggest:

1) Select a stiff column to minimize lateral deflection at the runway level.
2) Consider use shear key to take out shear force, and let the anchor rods to resist tension.
3) Provide braces in frames supporting runway rails, eliminate the need of moment connection at the base in that direction.

I think for a 5 ton crane, the measures above should be adequate to take care of the problems. You may consider utilize the concrete floor to provide resistance, just beware the details around the interface, as the column will vibrates and swings under the moving load, and the concrete slab tends to shrink away, and cracks.

You didn't answer my question, "

Quote:

Is there any reason why you can't bring the pile cap to the floor level?
". By doing so, the column will be shorter, and won't need protection for soil.

RE: Column Base Moment Connection

hokie's idea of a rigid portal frame seems viable to me.

What is the lateral force resisting system for the bridge crane in the existing bay? Could you tie the new framing into the old framing to piggyback on the existing LFRS? Maybe lattice the columns together. In conjunction with a portal frame, that could stiffen everything up considerably and reduce sway.

RE: Column Base Moment Connection

I agree with Hokie66, the moment at base and anchor loads can be too much plus you will have stiffness problem in the frame. A rigid moment connection, either by beam-col joint or better a brace between a beam above the crane and col would be efficient and more stiff for lateral loads and sway.

RE: Column Base Moment Connection

Serhiy2,

If you have headroom constrain for portal frame, here is one strong column option for your disposal.

RE: Column Base Moment Connection

1) I see some suggestions ref tying columns back to CMU wall.. we will NOT do this.. These tie backs experience dynamic & reversing loads... will cause cracks in CMU.
2) Someone mentioned 4 kip lateral load - This is way high for common 5 ton crane... assuming 1000# hoist....
11,000 (hoist & load)
x .2 (per AISC & ASCE)
x. 5 (1/2 of load to each side)
x approx. .925 (one ET wheel is over column, other wheel is XX ft towards next column down the runway)
yields 1,018#

3) This is the lateral force a free standing column & foundation will be designed for
I suspect things just got a bit simpler & smaller
But still DO not tie back to CMU wall
unless its a CMU double block column WITH rebar & full pour

4) Many commercial CMU wall buildings Ive seen have a double block & poured column on regular intervals along length of wall

We use simple W beams for this with runway beam simply bolted to top of column - no portal frame needed if there's a foundation being poured.
there have been shares of a spread sheet on this forum that sizes foundations with axial & moment loads
this is of course a moment loaded column


RE: Column Base Moment Connection

Serhiy2,
I don't know the distance between the short and long col on the right side of your sketch, bigger better, if they are aligned, you could tie them together with beams as moment connection and/or cross braces to resist lateral load from both cranes. Base anchors will have less tension due to wider foot print of two cols. Just a concept not sure about numbers.

RE: Column Base Moment Connection

If any suggestion to tie the interior columns, you should have a good understanding on the operation of both cranes, the interaction of two moving loads can be quite difficult to manage. If unavoidable, or somehow desirable, make the connection as flexible as possible, not rigid, otherwise it will tear apart very soon.

RE: Column Base Moment Connection

(OP)
My moments at column base are too high to be taken by moment connection because of column bracket is about 16" long so together with wheel load and p-delta analysis it adds up.

The way I got 4kip lateral load is from CISC Crane Supporting Steel Structures design guide by taking 40% of the load lifted by trolley.

I can't tie into the existing crane supporting structure because my columns won't line up and because existing structure uses roof diaphragm to bring loads to end walls.

I've decided to bring columns up to roof level and tie them to open web steel joist top chords with iron angles. Also, I will fasten columns located next to the firewall to the top of the firewall. This way wall will not experience any bending because it will be laterally supported on the other face by the building frame. Client will have to live with vibration if it happens.

Regarding the moment frame it would be nice but the beam on top of the columns would span 50ft so I would need some heavy section for that matter not to mention lateral bracing for it.

RE: Column Base Moment Connection

Can you grout the CMU wall solid, and stiffen it with reinforcing and a few bond beams along wall height.

RE: Column Base Moment Connection

(OP)
I will have it partially grouted and reinforced like every third core and bond beams one at the top and one mid-height I believe. Also, I won't be relying on wall bending in order to take crane lateral force so it should be fine regardless.

RE: Column Base Moment Connection

Sounds like you got good handle of situations. Good luck.

RE: Column Base Moment Connection

(OP)
Thank you for all the feedback. Have a nice weekend!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper - The Criticality of the E/E Architecture
Modern vehicles are highly sophisticated systems incorporating electrical, electronic, software and mechanical components. Mechanical systems are giving way to advanced software and electronic devices, driving automakers to innovate and differentiate their vehicles via the electric and electronic (E/E) architecture. As the pace of change accelerates, automotive companies need to evolve their development processes to deliver and maximize the value of these architectures. Download Now
White Paper - Model Based Engineering for Wire Harness Manufacturing
Modern cars, trucks, and other vehicles feature an ever-increasing number of sophisticated electrical and electronic features, placing a larger burden on the wiring harness that enables these new features. As complexity rises, current harness manufacturing methods are struggling to keep pace due to manual data exchanges and the inability to capture tribal knowledge. A model-based wire harness manufacturing engineering flow automates data exchange and captures tribal knowledge through design rules to help harness manufacturers improve harness quality and boost efficiency. Download Now
White Paper - Modeling and Optimizing Wire Harness Costs for Variation Complexity
This paper will focus on the quantification of the complexity related costs in harness variations in order to model them, allowing automated algorithms to optimize for these costs. A number of real world examples will be provided as well. Since no two businesses are alike, it is the aim of this paper to provide the foundational knowledge and methodology so the reader can assess their own business to model how variation complexity costs affect their business. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close