HSS Column Chord wall plastification
3

HSS Column Chord wall plastification

HSS Column Chord wall plastification

(OP)
While checking the moment connection for a W beam to HSS16x16x5/8 column we found out that the wall of the HSS column fails due to plastification. Can we spec a internal diaphragm plate as thick as the W beam connecting and get away with it.The arch wast to use the HSS for aesthetics and the utilization ratio of the column in 0.93 so we cant reduce the width of the column.

Is there any calculation that needs to be done to check the internal diaphragm plate ?

RE: HSS Column Chord wall plastification

How can you create an internal diaphragm plate? How does the welder get inside on both sides of that plate?

There are cases like this where you interrupt the column with a stub piece that has a plate on both sided. In those cases, the plates are continuous and the HSS column gets interrupted.

RE: HSS Column Chord wall plastification

I've tended to see a WT used as the shear plate in these instances as the flange of the WT is usually thicker than the HSS wall. You could just provide a plate welded to the column that is thick enough to span between sidewalls. I think diaphragm plates are going to be a fabrication nightmare.

RE: HSS Column Chord wall plastification

This is the connection I was thinking about. From the AISC Design Guide 24 on HSS connection. This Design Guide, by the way, is a must have if you are going to do a lot of HSS.

There are variations of this, of course. And, Jayrod's idea is a fine one as well... if the moment isn't too large.

RE: HSS Column Chord wall plastification

Just a random think, will a vertical extended end plate weld to the column work (if column is wider than beam)?

RE: HSS Column Chord wall plastification

You can disperse the flange force load causing HSS wall distortion by using one of the connections recommended in chapter 12 of the AISC Steel Construction Manual (pg 12-25&26 in 14th edition and pg 12-27&28 in 15th edition). If you really want to go with an internal diaphragm plate, your fabricator may give you pushback because it's the least economical/most costly option (because of the CJP with backing required to repair the HSS). I would only go with the internal diaphragm if the connection reinforcement can be fabricated entirely in the shop and the architect had rejected all other options.

RE: HSS Column Chord wall plastification

DrZ -

Yes, those connections should be much more economical. The one I proposed may only make economic sense for very high moments or seismic cases where you're trying to develop probably plastic moment.

RE: HSS Column Chord wall plastification

JP - Your recommendation would work out fine. I've used all of the connections cited, except for the internal diaphragm, which I avoid like the plague. I've had to observe NDT of field-welded CJPs, with backing, in HSS before and it's way more trouble than its worth.

RE: HSS Column Chord wall plastification

I dunno, I kinda like OP's detail if the joint is exposed and needs to look pretty. It seems to me that:

1) Most of the troublesome welds would be done in the shop and;

2) He's thought of the diaphragm weld access thing by having the HSS fabricated in two pieces and welded together after the diaphragms get installed.

3) It might be easier to hold the diaphragm plates in place during welding if the diaphragms were not full depth.

Quote (Avinash)

Is there any calculation that needs to be done to check the internal diaphragm plate ?

4) The diaphragm plates must not be allowed to compression buckle.

5) This might be easier to do with diaphragm welds as something other than full penetration welds. Whatever you do, make sure that it can move the diaphragm shears into the HSS side walls.

5) You still need to check shear, and shear buckling, of the HSS walls in between the diaphragms.

RE: HSS Column Chord wall plastification

(OP)
Thank you for all your valuable response, unfortunately we have moment connection all four sides and chord wall plastification is an issue on all four sides ( we had to rule out thru plate and External diaphragm plate). Can we suggest a cladding to the HSS?, in that case will the thickness of the cladding alone should satisfy chord wall plastification requirement or should the combined thickness of HSS wall + Cladding satisfy chord wall plastification.

Quote (KootK [
4) The diaphragm plates must not be allowed to compression buckle.

5) This might be easier to do with diaphragm welds as something other than full penetration welds. Whatever you do, make sure that it can move the diaphragm shears into the HSS side walls.

5) You still need to check shear, and shear buckling, of the HSS walls in between the diaphragms.)


I will do these checks and this is helpful

RE: HSS Column Chord wall plastification

It is your design, and you can do as you wish, but instead of pushing the HSS column to its limits and adding reinforcement, I'd either increase the HSS thickness or specify a box column made from grade-50 plate that can handle the loads. Anything to minimize labor costs and save you valuable time.

RE: HSS Column Chord wall plastification

@Avinash:. What document did those details come from?

RE: HSS Column Chord wall plastification

Latest post is straight out of the SCM. It's not the 14th edition (all figures of off by one but the content matches my page 12-27 exactly), so it's either the 13th or 15th.

RE: HSS Column Chord wall plastification

(OP)
Its from 13th edition steel construction manual.

RE: HSS Column Chord wall plastification

Thanks guys. The topmost of those four reinforcement details seems like a strange way to reinforce.

Quote (AvinashVeeresha)

Can we suggest a cladding to the HSS?, in that case will the thickness of the cladding alone should satisfy chord wall plastification requirement or should the combined thickness of HSS wall + Cladding satisfy chord wall plastification.

You might combine resistances for compression load delivery but not for tension load delivery unless you took deliberate measures to ensure that the cladding and HSS wall were adequately connected such that when you pulled on the cladding you'd also pull on the HSS wall.

RE: HSS Column Chord wall plastification

KootK - seems that would be a benefit of the topmost detail, wouldn't it? If the reinforcing angles are welded along the center line of the HSS wall, then the tension force is transferred through the cladding to the HSS wall at that weld.

RE: HSS Column Chord wall plastification

Still seems to me that the angle legs don't actually span across the HSS face that you're trying to prevent classification in. I'm sure it does something and, sized right, could do enough. I'd not look forward to trying to sort the numbers though.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper - Implementing a Multi-Domain System
IoT systems are multi-domain designs that often require AMS, Digital, RF, photonics and MEMS elements within the system. Tanner EDA provides an integrated, top-down design flow for IoT design that supports all these design domains. Learn more about key solutions that the Tanner design flow offers for successful IoT system design and verification. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close