Lateral Earth Pressure Question
2

Lateral Earth Pressure Question

Lateral Earth Pressure Question

(OP)
I'm doing a preliminary analysis on a buried structure from the early 1960's.

Reviewing a Geotech report from the same site and they are recommending a lateral at-rest pressure of 60 pcf above the GWT and 100 pcf below the groundwater table. Then they have this tidbit: "The values calculated for the above parameters would provide ultimate values. We recommend a minimum factor of safety of at least 1.5 be applied to the calculated lateral values."

Help me interpret that. If I apply the loads (60 and 100 pcf) to a wall and I'm interested in the forces in the concrete would I need to add the 1.6 load factor per ASCE 7 or would that be double dipping?

RE: Lateral Earth Pressure Question

I believe those values were un-factored from soil test results, so required a safety factor of 1.5 in performing analysis for bearing, sliding, and overturning.

Are you checking the stability of an existing structure/retaining wall, or with the intent to perform modification/rebuilt?

RE: Lateral Earth Pressure Question

(OP)
No, I'm trying to check the existing reinforcing in the walls as we are making some changes to the structure. The structure is a buried wet well so there really are no unbalanced forces that would create overturning or sliding.

I've created a FEM and applied the 60 and 100 pcf loads and then applied the 1.6 load factor per ASCE7. The moments produced exceed the capacity using the rebar size and spacing from the existing plans. I'm in the process of sharpening my pencil and that "ultimate value" statement stuck out to me.

RE: Lateral Earth Pressure Question

I believe the original design was done using 90 pcf and 150 pcf, respectively, and by Allowable Stress Design method. Does the wet well has concrete cover on top? And have you checked the wall as edges supported plate - a common practice at that time using Bureau of Reclamation engineer mono plates.

RE: Lateral Earth Pressure Question

(OP)
It does have a concrete top. We are looking at taking that off. There are also some intermediate steel beams that I'm just not sure what their purpose is. We'd also like to get rid of those.

I'm in the process of checking it with the Bureau of Rec tables.

RE: Lateral Earth Pressure Question

I made mistake on stating 90/150, which shall be 60 and 100 respectively. As the safety factor concerns stability analysis only. Consider a soil weights 120 pcf, Ko = 0.5, the 60 pcf makes sense, as well as the 100 total weight below water table.

RE: Lateral Earth Pressure Question

(OP)
So then you're thinking for strength design of concrete a 1.6 load factor would be appropriate? And the 1.5 FS would be for checking stability...?

RE: Lateral Earth Pressure Question

I'll start with checking a propped beam spans vertically, using ASD and fy = 40ksi. How the steel beams were attached, structurally speaking?

RE: Lateral Earth Pressure Question

Rabbit12 - When in doubt, check with the author of the report. You don't want to accidentally over or under apply the factor of safety.

Usually its a FOS of 1.5 on sliding, 2-3 on overturning, and 2-3 on bearing capacity. But if they gave you an allowable bearing pressure you can just use that instead of calculating the ultimate and factoring.

RE: Lateral Earth Pressure Question

(OP)
retired13, attached is a picture of the steel beams. I'm not sure they are original as they don't show up on the original plans. The existing well is 15' square and 28' deep so really mostly one way action horizontally.

MTNClimber, I plan to try to contact the report author but it's two days after xmas and no one is around. I'm just doing a preliminary design so thought someone could possible shed some light on the "ultimate value" they reference. Again, I'm not concerned about a stability analysis or bearing since it's buried on 4 sides and we aren't adding any gravity loads. I'm concerned about the concrete walls since we want to tear the lid off and pull those intermediate beams out. I don't know if the original designer intended for those elements to help redistribute some moment in the concrete.

RE: Lateral Earth Pressure Question

I only factor lateral earth pressures if I'm working in LRFD. I, personally, wouldn't factor loads using ASD. I'm having trouble as to why they would say to factor those loads by 1.5 (which is how I'm interpreting the language). Sounds like its typical language for them. If its urgent, maybe any senior engineer present in the office can help?

RE: Lateral Earth Pressure Question

(OP)
MTNClimber, I guess I'm kind of interpreting it differently. I think they are saying the lateral earth pressures they are giving are ultimate. Normally that would mean I wouldn't factor the loads when checking the concrete using LRFD.

It's not particularly urgent. I thought maybe someone on here would have seen that language before since I'm the only one here today. I've been doing this for awhile (actually am a senior engineer which means I must be sounding dumb......bigsmile) and I can't recall ever seeing that verbiage.

RE: Lateral Earth Pressure Question

I 100% agree that the language is abnormal and confusing. Those values line up for a soil with a friction angle of about 32 degrees. Unless the retained soil is very dense sand and gravel I wouldn't consider using a lower value. I would factor those loads for LRFD but not ASD, as factoring lateral earth pressures in ASD doesn't make sense to me (unless its concrete design).

RE: Lateral Earth Pressure Question

The steel beams are quite heavily built, don't looks like scaffold for repair works. Is there a large opening to get the beam in, or the beam is spliced inside? I would carefully exam the wall and slab to see if there any indication of large cracks and old repair works, also bulging. For the beams were not shown on the drawing, and obviously not supporting any equipment, I can only guess the wall had experienced excessive load (could be unexpected flood, or construction load), and the beams were there to prevent the walls from cave in. But why only one way?! I am puzzled.

RE: Lateral Earth Pressure Question

The aspect ratio is approximately 1:2, so two way action is possible. For one way action, make sure to check both fixed-fixed and pinned-pinned to get maximum moments for both faces.

RE: Lateral Earth Pressure Question

The loads seems fairly straightforward. The 60pcf and 100pcf are fairly typical nominal (expected, unfactored, sometimes termed ultimate) loads (see below). In the original design, it appears that the FOS was directly 1.5 (equivalent to an ASD reduction factor of 0.67). How you provide a FOS depends on what design method you're going to use.

ko*gammasoil = 0.5*120pcf = 60pcf
kosubmerged*(gammasoil-gammawater)+gammawater = 0.6*(120pcf-62.4pcf)+62.4pcf = 97pcf

Rod Smith, P.E., The artist formerly known as HotRod10

RE: Lateral Earth Pressure Question

The OP said the geotechnical report stated "The values calculated for the above parameters would provide ultimate values. We recommend a minimum factor of safety of at least 1.5 be applied to the calculated lateral values.". I'm guessing that has nothing to do with the original design. It's such a vague statement that it needs further clarification. My honest guess is that the geotech doesn't know what they are talking about either.

RE: Lateral Earth Pressure Question

Isn't that the geotechnical guy used to get soil strength at failure, divide by a safety factor, then hand to the foundation guy to check soil reaction due to service load?! Note, that often times, the same word but its usage and meaning are quite different among disciplines. And that's where confusion roots.

RE: Lateral Earth Pressure Question

Retired13 - I'm not quite following what you're trying to say but I hope this addresses your question/statement. In order to develop the lateral earth pressure recommendations, the geotechnical engineer would look at the soil classification and blow counts to estimate a soil strength or use strength testing in order to develop lateral earth pressures. Those values, which are not factored (but can be, see next paragraph), are provided to the designer. The designer would then design the retaining structure using the appropriate factor of safeties using ASD or factor the loads and resistance values using LRFD. The geotechnical report should not be listing an arbitrary factor safety. If it is going to provide a factor of safety, it should be clear as to what the factor of safety is being applied to or, what is typically done, not list one at all.

In my experience, geotechnical engineers try to be slightly conservative when providing lateral earth pressures. Typically budgets on jobs don't allow for a large strength testing program which can give a clear indication of the soil strength across the site for each soil type. We generally look at the soil type, blow counts, and past experience to estimate the soil's strength. I'm sure a lot of the soil I provide recommendations for could have a higher strength, but unless the client wants to pay to find out, I'm not going to give the higher values to the designer.

RE: Lateral Earth Pressure Question

MTNClimber,

I agree with you that, in this case of lateral earth pressure concern, the geotechnical guy was not likely to factor the load up or down, but to emphasis the resulting structural reactions need to maintain a safety factor of 1.5, which in turn resulted in a material strength capacity reduction factor of 1/1.5 = 0.67, that was close to 0.66 required by code, using ASD method. I believe the word "ultimate" was meant soil state at test, nothing to do with "ultimate strength design" (USD). So, same word, two definitions.

Also, I don't think LRFD is a proper term for reinforced concrete design, though the efforts and results are comparable. Maybe I am outdate though.

RE: Lateral Earth Pressure Question

Don't confuse strength reduction factors (Φ factors) with safety load factors...two completely different things that are focused and based on different variabilities.

Φ factors are based on the variability of the material properties as well as the variability of the equations that we use to derive strength (resistance) of our structures.
Load factors (sometimes called safety factors) deal with variabilities in the predicted loads.

Load factors turn actual/service level loads into ultimate loads....unless the load is already an ultimate load (i.e. seismic loads).

The geotech here, I think, is trying to say something but turned it completely around.
1. They call their 60/100 load an "ultimate load" but,
2. They then say that you need to kick UP the ultimate load by a load factor, to make it....more ultimate?

They should have instead said: "The values calculated for the above parameters would provide actual service level values. We recommend a minimum factor of safety of at least 1.5 be applied to the calculated lateral values."

RE: Lateral Earth Pressure Question

JAE, the approach you outline is what would be done for a new structure under LRFD design, but if the geotech is using the approach we do in structural design when dealing with an existing structure (evaluate or design under the original design criteria), then the given values would be those for ASD. For buried structures under ASD, it's fairly common to have ultimate (expected) loads compared to expected capacities, and the capacity must be greater than the load by a certain margin (FOS). In this case, the recommended FOS was a factor of 1.5. That's how it looks to me, anyhow.

Rod Smith, P.E., The artist formerly known as HotRod10

RE: Lateral Earth Pressure Question

(OP)
All, I should clarify. The Geotech report I'm using for these lateral values is a much newer report and not specifically for this structure. There are several structures on this site built at different times. Since I have no information as to what the existing structure was designed to, I'm starting by using the values in that report since it's reasonably close to this structure.

JAE, the Geotech report isn't saying kick UP their loads specifically, but if I'm following section 2.3.2 of ASCE 7-10, the load factor for an H load is 1.6 for most load cases. I have always considered the maximum forces/reactions/ etc. from LRFD load cases ultimate. When I was getting moments well above what the existing rebar could handle I started to question that statement because I found it odd.

Retired13, there is an existing 4' square hole that has a spiral stair that possible could have been used to get those beams in, but getting them rotated into place would have been difficult. And yes, they are only in one direction and at least one has been almost completely cut (just one flange remains) because it was evidently in the way of a pipe. There was at one time a platform that at some point was mostly taken out (some random pieces still remain). You're comment about the usage of the same word across disciplines is funny, trying to explain to a mechanical pipe stress engineer why he can't just simple add everything together and give me loads is trying at times.

BridgeSmith, I agree the values seemed reasonable to me given the soil types (CL and SP mostly).

RE: Lateral Earth Pressure Question

Quote (JAE)

The geotech here, I think, is trying to say something but turned it completely around...
2. They then say that you need to kick UP the ultimate load by a load factor, to make it....more ultimate?

That would result in "double dipping" and creating an overly conservative design. If that is what they are saying, I would challenge that recommendation.

RE: Lateral Earth Pressure Question

Don't confuse load factors with factors of safety. The geotech is saying to use a safety factor of 1.5. Therefore, this would be for allowable stress design. ASD requires no load factors and no resistance factors. If the at-rest equivalent fluid pressure is 60 or 100 pcf, these seem like service load earth pressure or combined earth and water pressures. Use the service loads and compare the driving forces to the resisting forces to see if you have the 1.5 safety factor for sliding and overturning. For designing the actual structure, factor up the 60 and 100 pcf appropriately to perform the LRFD or LFD design. Remember that the 100 pcf pressure includes water pressure. The earth pressure and the water pressure usually have different load factors. Therefore, the 100 pcf may need to be broken up into the soil portion and the water portion so that the different load fctors can be properly applied.

www.PeirceEngineering.com

RE: Lateral Earth Pressure Question

Rabbit12,

It looks like the beam were got in before the cover was casted. It could have been utilized to hoist equipment, or materials, and left there. But it puzzles me that the beams do not look aged, and there are no anchors at the ends (couldn't tell from the photo). So I can only think they are for temporary purpose. Well, since they are only a few feet from the cover, unless you are positive they are not for support, you may want to excavate a few feet below the level of the beams to relieve the pressure, then carefully remove the beams. Who knows, the beam might just drop to the bottom during excavation :)

For concrete check, the lateral pressures are reasonable, you should use ASD, not USD, although the result should be satisfactory using either method. Keep in mind, this structure has been there a little more than half of a century, we have to ask "why it is no good now?".

RE: Lateral Earth Pressure Question

For lateral demand on a wall, expected pressure = service pressure = ASD.
I would not use "ultimate" as a synonym for expected. For this discussion using ASCE 7 as the basis, I would avoid the term ultimate.
ASCE 7 approach:
For sliding and overturning stability, use service loads (service load combos) and compare with expected resistance provided by the soil (friction, bearing, passive). The factor of safety is the ratio.
For the reinforced concrete design, use factored loads as the demand. Compare with φPn, φMn, φVn...
Do not use factored loads and then compare to resistance with a factor of safety.

RE: Lateral Earth Pressure Question

(OP)
Retired13, there are anchors on the beams. They are just inside the flanges and barely visible in the photo I attached. There are steel members at two elevations, see attached second photo. These beams also support some platforming that's been butchered over the years.


You're right about this structure it's been working for almost 50 years. However, we are proposing changes including taking out the steel beams and taking the cover off the top (and replacing it with an intermediate floor). I have to make sure our modifications don't damage the existing walls. Leaving the existing steel in place isn't an option since this is a WWTP and they would quickly corrode.

RE: Lateral Earth Pressure Question

(OP)
I should add, the walls look great. No visible cracking or other signs of distress.

RE: Lateral Earth Pressure Question

You are in the correct path - gather information and evaluate the strength of an existing structure. I think result from BOR mono graph will provide the confidence you are seeking. After seeing the new photo, I don't think there is much problem to remove the beams, and take out the cover, provides the structure is properly braced/supported at strategic locations at all time, until completion of the permanent lateral support.

RE: Lateral Earth Pressure Question

Instead of waiting for the mono graph, you can model the wet well as plate element and apply the loads to get the results.

RE: Lateral Earth Pressure Question

Quote (Rabbit12)

JAE, the Geotech report isn't saying kick UP their loads specifically...
Yes they are - read what they wrote: We recommend a minimum factor of safety of at least 1.5 be applied to the calculated lateral values." They are saying to kick UP the loads by 1.5.

Quote (BridgeSmith)

...when dealing with an existing structure (evaluate or design under the original design criteria)
I don't agree that you should evaluate the current structure based on older codes, methods, etc. You should use the applicable, legally accepted provisions that apply now.

Also - the original geotech called them "ultimate" loads.
So with a factor of safety added either you are double factoring already "ultimate" loads or you are reducing an ultimate load to a service level load - and then you would use ASD with OTHER safety factors to get it right.

The original geotech called them ultimate loads and then said to apply a 1.5 "safety factor" to those ultimate loads. That is simply BS and wrong.

I stand by what I wrote above - and in bold - as to what the geotech should have said.

He obviously intended the 60 pcf to be factored UP to 90 pcf....thus the 60 pcf is a SERVICE load and not an ultimate load.

RE: Lateral Earth Pressure Question

Quote (JAE)

I don't agree that you should evaluate the current structure based on older codes, methods, etc. You should use the applicable, legally accepted provisions that apply now.

I don't care to debate whether the current code or original design code should be used in the analysis of existing structures, mostly because I don't have a strong opinion on that one way or the other. In our office at the DOT bridge design section, the decision to do analysis and design for rehabilitation under the original design code was made above my level. I was merely stating my supposition that perhaps the geotech had approached it that way in preparing the report, which seems consistent with the terminology used.

Quote (JAE)

I stand by what I wrote above - and in bold - as to what the geotech should have said.

I agree the geotech mixed terminology from different design methods. However, I'm not sure I can agree with your bolded statement. It also seems to mix terminology between design methods. To my knowledge, only LRFD uses 'service load', but it does not use safety factors.

To be consistent with an LRFD approach, the loads should be reported as 'nominal' and the 1.5 as the recommended load factor. Although, my understanding of the AASHTO LRFD design method would indicate the geotech should stay mum on the factors and let the specifications dictate the proper factors to use.

To be consistent with ASD, if my memory serves, the load would have no modifiers - just list the soil loads as 60pcf and 100pcf, and leave safety factor verbiage as is.

Rod Smith, P.E., The artist formerly known as HotRod10

RE: Lateral Earth Pressure Question

(OP)
JAE, I guess I can see how you could say he's saying that the 60 pcf and 100 pcf are ultimate loads and then adding an additional FOS of 1.5. I guess I interpreted that 1.5 as the FOS for stability checks. Which I guess says we have more ambiguity.

BridgeSmith, working for a state DOT I would think puts you in a different position when evaluating older structures than myself. It seems reasonable to do what you are describing when you own the structure. We are required to utilize the current design code. I have used the provisions in the IEBC a ton to prove existing structure are adequate because it's virtually impossible (especially in seismic country) to get old structures to work under newer codes when adding loads or modifying.

I also should reiterate that this Geotech report was for a new structure near this existing one on the same site. It's all I have right now to go on so was using it. This report had nothing to do with the existing structure so saying that the language was trying to align to the actual design code isn't correct.

FWIW, I contact the Geotech for clarification on the language. The response verbatim was, "There is not a safety factor added to the equivalent fluid pressures provided.". No attempt to explain the verbiage at all. To add to this, our client likes these guys and is making us use them for the new project we have. I'm pretty stoked to work with them.thumbsdown

RE: Lateral Earth Pressure Question

If they give you the same language in the report for this job, I'd make sure to write up your questions and CC the client as it helps the client understand when one of their engineers are being unclear and/or wasting everyone's time.

RE: Lateral Earth Pressure Question

Quote (Rabbit12)

...this Geotech report was for a new structure...

Sorry, I seem to have missed that in the previous posts. Well, that theory is shot down, then. It seems to be just poor use of terms by the geotech, then.

Quote:

We are required to utilize the current design code. I have used the provisions in the IEBC a ton to prove existing structure are adequate because it's virtually impossible (especially in seismic country) to get old structures to work under newer codes when adding loads or modifying.

That's one of the reasons we use the code it was designed under; so that we don't end up in the pickle where the bridge is ok as long as we don't look at it, but if we look at it per the new code, it's substandard. The other main reason is that having different components of a bridge designed under different codes adds unnecessary cost and creates difficulties in load rating.

Anyway, back to the OP. The way I read it, and still understand it, the 60pcf and 100pcf are what would normally be termed "nominal", or to use one of the words they used, "calculated" loading (i.e., no factors applied).

If it was me, I would ignore the 1.5 FOS they "recommend", and apply the load and resistance factors per the governing design code.

Rod Smith, P.E., The artist formerly known as HotRod10

RE: Lateral Earth Pressure Question

I don't know when the argument of the lateral loads are "ultimate" or "service" started. To me it is clear, as usually sandy material has a unit weight of 120 pcf, water 62.4 pcf, ko (at rest) = 0.5, thus the soil above water table, ϒs= 0.5*120 = 60 pcf; and below water table, ϒTOT= ϒb+ ϒw= 0.5*(120-62.4)+62.4 = 91.2 ≅ 100 pcf (cal done by Rod previously). Since no factors were applied, thus the loads are "service loads".

I could be wrong, but I am holding my believe, that given the same load, ASD will yield a result more conservative than USD, in another word, design done by ASD shall have no problem to meet USD strength requirements.

RE: Lateral Earth Pressure Question

Also, the reason I suggested to use ASD to check the existing structure is, because if done correctly, you shall get the exact capacity as the original design. Otherwise, you may have done something wrong. USD can't tell this, unless you are willing to accept the "not that close" capacity literally.

RE: Lateral Earth Pressure Question

(OP)
retired13, the argument started because of the language in the report. They explicitly state, "The values calculated for the above parameters would provide ultimate values." The only values above that statement are the lateral earth pressures. I asked the question because the statement is odd to me and doesn't make sense because the loads (60 pcf and 100 pcf) seem reasonable to me.

As far as analyzing the concrete, I did check it using the Bureau of Rec tables and a FEM. Both show the concrete failing, but I'm assuming rebar strength (40 ksi), concrete strength (3 ksi), and the loading is likely not what was used for original design. The unity levels are over 1.5. Given the fact this structure is 50 years old and is in great shape, I'm confident my conservative assumptions are the culprit.

So I've actually resorted to doing a comparison between current condition and our proposed condition. In certain elements, our forces increase around 1-1.5%. I'm ok with that.

RE: Lateral Earth Pressure Question

In my experience, geotechs usually recommend minimum service loads for design and then leave the actual design to others. Geotech are not usually known for their structural design expertise. How can someone specify an "ultimate" load if the structure has not yet been designed? The geotech for this project needs to define "ultimate." If the geotech thinks that "ultimate" means "factored," then what design code (AASHTO, IBC, etc.) and load factor were used in the recommendation? I never see geotechs recommend factored design loads. At the risk of starting a heated debate here with geotechs, I don't usually pay too much attention to what most geotechs say when they "recommend" design procedures or specify how to do structural design. I'm sorry if I insulted any geotechs.

www.PeirceEngineering.com

RE: Lateral Earth Pressure Question

Quote:

Both show the concrete failing, but I'm assuming rebar strength (40 ksi), concrete strength (3 ksi), and...

Weren't the rebar and concrete strength indicated on the drawing (I assume you've the drawing otherwise you wouldn't know the As and pattern)? I'll make the same assumptions as you did. But now, since all methods indicate falling, it is time to dig a little deep into it, because if I am the owner, I might buy into that logic that says "it has been there for...", but then turn my head and say "gee...!".
Since the cover is to be removed eventually, I suggest to take this opportunity to take a core sample, and have a lab analyze the rebar and the concrete.

Quote:

and the loading is likely not what was used for original design.
Why? What you think likely had been used?

Quote:

The unity levels are over 1.5.
I don't understand where you get the "utility level", can you elaborate further?

RE: Lateral Earth Pressure Question

(OP)
Retired13, the rebar and concrete strength was not in the drawings hence the assumption. I'm not terribly surprised that information isn't shown. I've done lots and lots of existing modifications and it's a crap shoot whether that information is shown. It's also possible that sheet is missing. Thankfully I had section width and rebar layout to use.

I have no idea what loading they used in 1962. The drawings don't show anything so it's another variable in my analysis. Likely leading to my trouble making the structure check out on paper.

Not sure what's confusing on the unity. Mu/Mallow.

I don't agree that we need to dig into this deeper. As you stated earlier, the structure has worked for almost 50 years. I've analyzed the changes we are making and they are acceptable when compared to the original in place structure per an adopted code (2018 IEBC) why would I take this any further? Asking the owner to spend several thousand dollars just to prove something on paper seems like a waste.

RE: Lateral Earth Pressure Question

I wouldn't think it (core sample) is a waste, if I am expecting to do more works in the same yard and for the same owner. But it's your project. I drop my case.

RE: Lateral Earth Pressure Question

I got the word "utility" now, thanks. But here is my little note, historically ACI USD load factors were:

DL - 1.5 (early 60s), and 1.4 (since 70s)
LL - 1.8 (early 60s), and 1.7 (since 70s)

I consider lateral earth pressure and hydrostatic pressure both are live load. Since no dead load is involved in the design of the wall, the utility number should be greater than 1.5. Agreed?

RE: Lateral Earth Pressure Question

I retract my last post. Your finding makes sense.

RE: Lateral Earth Pressure Question

Quote (PEinc)

I don't usually pay too much attention to what most geotechs say

How dare you... just kidding.

Some of the best geotechs I've worked with could do both (relatively basic) structural design as well as geotechnical work. Actually, my university didn't offer enough graduate classes to only take geotechnical courses so most of us took 1/2 geotech and 1/2 structural graduate courses. Geotechs that could do structural design seemed normal to me until I moved west. And now I'm very grateful for my "geo-structural" background. It helps me to get more work but also helps me translate concepts to either my boss or to the structural engineer on the project. I personally wouldn't want it any other way.

RE: Lateral Earth Pressure Question

Quote (MTNClimber)

Some of the best geotechs I've worked with could do both (relatively basic) structural design ...Geotechs that could do structural design seemed normal to me until I moved west. And now I'm very grateful for my "geo-structural" background.

I'm on the other side of that - I'm a structural trying to muddle my way through doing half of what a geotech would normally do (without any formal training in it), because our DOT only employs geologists and structurals.

Rod Smith, P.E., The artist formerly known as HotRod10

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper - How ESI is Helping Move New Medical Device Product to Market Quicker & More Cost Effic
Early Supplier Involvement has long been a strategy employed by manufacturers to produce innovative products. Now, it almost seems like a necessity. Because decisions made in the design phase can positively affect product quality and costs, this can help add value to OEM bottom lines. This white paper will discuss many facets of ESI, including why it’s so valuable today, what challenges limit the benefits of ESI, how cost is impacted, and more. Download Now
White Paper - Moving to a Driverless Future
This white paper describes what we see as the best practices to support a sustainable engineering process for autonomous vehicle design. It exposes how to use simulation and testing in common frameworks to enable design exploration, verification and validation for the development of autonomous cars at a system, software and full-vehicle level to drive a mature product development process for automated driving. Download Now
Research Report - How Engineers are Using Remote Access
Remote access enables engineers to work from anywhere provided they have an internet connection. We surveyed our audience of engineers, designers and product managers to learn how they use remote access within their organizations. We wanted to know which industries have adopted remote access, which software they are using, and what features matter most. Download Now