passing two 0-10 VDC signals in one four conductor shielded cable?
4

passing two 0-10 VDC signals in one four conductor shielded cable?

passing two 0-10 VDC signals in one four conductor shielded cable?

(OP)
Hi,

I am working on a project in which I have to pass two separate 0-10 VDC signals between a PLC and a dedicated function controller. One of these 0-10 VDC signals is used to transmit a set point from the PLC to the dedicated function controller. The second 0-10 VDC signal is used to transmit the measured process value from the dedicated function controller to the PLC.

I am wondering if it would be safe to use a single four conductor shielded cable to pass these signals back and forth (using two conductors for each signal), or whether I should be concerned about these signals interfering with each other?

Any advice will be greatly appreciated. Thanks in advance.

Best regards,
Paul

RE: passing two 0-10 VDC signals in one four conductor shielded cable?

There should be no concern of two 0-10VDC signals in adjacent wires interfering with each other. This would normally be done with three wires using a common zero reference wire. Shielding to exclude outside interference is good practice. It is important to avoid any ground loop currents in your signal wires.

RE: passing two 0-10 VDC signals in one four conductor shielded cable?

I agree with Comp. Especially if neither signal is rapidly varying.

Keith Cress
kcress - http://www.flaminsystems.com

RE: passing two 0-10 VDC signals in one four conductor shielded cable?

CompositePro - use of a common return makes the assumption of a common ground at both ends. It also introduces the possibility of intermodulation of one signal onto the other due to IR drop in the common return. Depending on the accuracy involved it's possibly not worth the saving of one conductor. There are also disadvantages of running two separate grounds between two common points, so it's a design decision to work out which compromise is the least bad.

Is there any reason why 4-20mA can't be used, which addresses some of the problems noted above?

RE: passing two 0-10 VDC signals in one four conductor shielded cable?

(OP)
Hi ScottyUK, CompositePro, and Keith,

I just wanted to thank you for your help on this question, and I apologize for my delayed response. 0-10 VDC was my only option because the devices for which I am using these signals do not support 4-20 ma. It did cross my mind that I might be able to use a common return, but the device literature did not make it clear the the common terminal for the remote set point feature and the common terminal for the measured process value are internally connected. The terminals were labeled differently - one as "TEN RTN" and one as "GROUND". I figured I wouldn't take any chances and used a dedicated conductor for each. Anyway, it worked! Your responses gave me the confidence to give it a try. I appreciate your help!

Best regards,
Paul

RE: passing two 0-10 VDC signals in one four conductor shielded cable?

I commend your choice. Just your time thinking about it was more expensive than the added wire.

Keith Cress
kcress - http://www.flaminsystems.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper - Addressing Tooling and Casting Requirements at the Design Stage
Several of the tooling and casting requirements of a part can be addressed at the design stage. If these requirements are not addressed at the design stage, lot of time is spent in design iteration when the design reaches the die caster. These design issues lead to increase in time and cost of production leading to delay in time to market and reduced profits for the organization. Download Now
White Paper - The Other Side of Design for Assembly
Assembly level constraints need to be satisfied before the design can move downstream. This white paper will go through the various assembly level issues, which need to be tackled by various organizations on a regular basis. Know more about DFMPro, a design for assembly software. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close