design of base plate on axial tension plus moment loads

design of base plate on axial tension plus moment loads

design of base plate on axial tension plus moment loads

(OP)
Dear experts

AISC Design guide-1 for design base plate and anchor rod is concentrated only on the applied axial compression plus moment loads, even in the two methods (uniform and triangle) of design the base plate, my question is , shall i use these two methods in case of axial tension plus moment or these methods are not applicable for this case .

Thank you

Thank you

RE: design of base plate on axial tension plus moment loads

Seems to me that axial tension won't affect the base plate, but only the anchor rods. Draw the FBD of the resultant force if you have tension and moment combined in your connection. The tensile side of your moment will be additive with the tension in the column and will pull on your anchor rods with a greater force. The base plate shouldn't be affected.

RE: design of base plate on axial tension plus moment loads

I agree with NetTension that the anchor rods will see the combined flexural tension plus direct tension. I disagree that it won't affect the base plate.

Presumably, the tension from the connected element to the anchor rods is resolved through flexure of the base plate. More tension in the rod equates to more flexure in the base plate. If the anchor bolts sit on chairs or straddle the connected element then them effect on the base plate might be minimal. It all depends on geometry.

You just need to look at the load path and figure out where the loads go.

RE: design of base plate on axial tension plus moment loads

That was an oversight on my end JLNG of course an increase in tension force in the rods needs to be reacted somewhere. Most likely in the base plate. Try this Link. See also page 25 of DG1, which describes how to handle tensile axial loads "For tensile loads, a simple approach is to assume the an-chor rod loads generate bending moments in the base plate consistent with cantilever action about the web or flanges of the column section (one-way bending)" (AISC DG1). This is only for the case where your anchor rods are outside of the column flanges. For the case where anchor rods are inside of the flange two-way bending must be considered.

RE: design of base plate on axial tension plus moment loads

Direct to your question:

1) For large moment that resulted in only a pair of anchors in tension, I think the case from DG1 is still applicable.

2) For small moment that resulted in all bolts are in tension, I suggest to add some weight to counter the lift force. As this case is not well addressed in literatures, as long as I can remember. (Note that net tension case does not apply, because part of the base plate will still in contact with the floor, prying action will occur)

RE: design of base plate on axial tension plus moment loads

I’m not sure I agree that all bolts in tension aren’t covered in literature, because DG1 directly addresses the case as I quoted. Do you disagree retired13?

Edit: this is a question not a challenge

I just enjoy the debate

RE: design of base plate on axial tension plus moment loads

NetTension,

No, I wouldn't suggest that is well covered, as the word, "assumed bending line" (Fig 3.1.1) is vague to me. The method DG1 employed was a modification to the ultimate strength design of reinforced concrete, with a pair of anchor bolt in tension, and a compressive stress block under the column compression flange. It works fine as the case I stated in my comment #1 above, but when all bolts are in tension, that is liking both top and bottom reinforcing steel are all in tension, how does that compressive stress block look then? That's the reason I wouldn't suggest it without further understanding. I think evaluation of prying action maybe one way to go, and FEM is another, if exact solution is desired.

RE: design of base plate on axial tension plus moment loads

If case 2 in my comment is the predominate case in your design, as suggested, add weight to diminish the lift force, or modify you framing, so the structure is not standing on its toes.

RE: design of base plate on axial tension plus moment loads

For simplicity, I use a rectangular stress block for compression.

Dik

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close