New deck joists sistered to existing cantilevered joists?
I am working on a project, 2 story residence with an existing 8 to 10 foot cantilevered deck. All wood framed construction in Southern California. The existing floor & deck consists of 2x10 DF joists that sit directly on top of 11-7/8" TJI joists. The first span is 18ft, which is the interior house floor & then they both cantilever from 8 to 10ft as an exterior deck. Please refer to the attached pdf that shown the existing and proposed condition.
If I sister new deck joists spanning the full new deck length to the existing 2x10 upper deck joists and remove the lower TJI joist at the deck I have some concerns about the actual loading to the new beam supporting the deck and wall above.(noted on attached pdf). Note that there is also a new wood framed shear wall approximately 16 inches behind the new dropped beam, so not the existing 2x10 will be a multi span condition.
The reaction for this condition is what you would expect with a larger gravity reaction on the wall and an uplift over the beam.
The more I think about this solution the more I think that there may be another better/cleaner solution.
What are your guys thoughts, opinions?
RE: New deck joists sistered to existing cantilevered joists?
Also, can the existing 2x10 joists support the shearwall load at the location noted? I feel like 2x10 spanning 18ft are pushing the limits at the best of times, throw in a point load and you're asking for trouble.