Oct 4, 2019 #1 Kani77 Electrical Joined Feb 25, 2014 Messages 21 Location CA Hi, Do wee need to use stress cones (Termination kit) for MV Tray cables 4.16kV and 23kV. Please share your knowledge and recommendation. thanks, Kani
Hi, Do wee need to use stress cones (Termination kit) for MV Tray cables 4.16kV and 23kV. Please share your knowledge and recommendation. thanks, Kani
Oct 6, 2019 2 #2 cuky2000 Electrical Joined Aug 18, 2001 Messages 2,135 Location DO Yes, Cable termination (stress cones ) for 4.16 & 23 kV system should be installed to manage the excess of electric fields created at the cable end. Below is an example of the EMF Stress release with & without cable termination. Upvote 0 Downvote
Yes, Cable termination (stress cones ) for 4.16 & 23 kV system should be installed to manage the excess of electric fields created at the cable end. Below is an example of the EMF Stress release with & without cable termination.
Oct 7, 2019 Thread starter #3 Kani77 Electrical Joined Feb 25, 2014 Messages 21 Location CA Thanks cuky2000!Much appreciate your reply. Upvote 0 Downvote