Transformer sizing crieteria
Can someone guide in calculating transformer size for 1 mega watt DC motor with following specs.
Power: 1 Mega watts
Rated voltage: 700
Base RPM: 30
Field current: 240 Amps
Rated current: 1700 Amps
My application is plate rolling mill where current goes up to 3600 ampere, that is where we have set our High speed circuit breaker. Earlier this application was running with MG set, it is a reversible rolling mill.
RE: Transformer sizing crieteria
Stick with the MG set.
You can't run a DC motor directly from a transformer.
You will need an electronic drive to feed the motor if you ditch the MG set.
The drive will need to be oversized to handle overloads of 200%+.
The drive manufacturer may want a special transformer or may supply the transformer as part of the drive.
The drive manufacturer may want a 6 phase or 12 phase output to reduce ripple and harmonics.
The drive manufacturer may want a transformer with a specific impedance.
For a new installation, consult the drive manufacturer for transformer specs.
Consider also an AC VFD drive. Again, consult with drive manufacturers.
For an existing installation, repair the MG set.
Bill
"Why not the best?"
Jimmy Carter
sorry waross I could not provide the full information, actually it is an up gradation project where we are replacing MG set with a 4 quadrant dc drive with 5000 amperes armature current. The drive supplier is also responsible to provide rectifier transformer with 2 secondary winding of one star/delta each. But the rated power for above transformer is 3 MVA which seems high for 1 mega watt dc motor, so i wanted to know how the sizing should be calculated, considering safety margins etc.
3MVA doesn't seem particularly oversized considering what you have posted.
5000 Amps x 700 Volts = 3,500,000 Watts = 3.5 MW.
(5000 Amps + 240 Amps Field) x 700 Volts = 3.67 MW
3.67 MW x 1.25 = 4.6 mW
4.6 MW / unknown distortion PF = 5 MW
I agree with Lionel.
Bill
"Why not the best?"
Jimmy Carter
Thank you very much and sorry for the late reply
Click Here to join Eng-Tips and talk with other members! Already a Member? Login
Research Report - How Engineers are Using Remote Access
Remote access enables engineers to work from anywhere provided they have an internet connection. We surveyed our audience of engineers, designers and product managers to learn how they use remote access within their organizations. We wanted to know which industries have adopted remote access, which software they are using, and what features matter most. Download Now
eBook - Managing the Context of Product Complexity Using the Digital Twin
Keeping track of changes to complex products is difficult—think Aerospace & Defense equipment, new generations of commercial aircraft, and software-based automobiles. A new way to managing the digital context of the physical product is required and the answer is the Digital Twin. This ebook explores the opportunity available for Operations and Maintenance for the Digital Twin. Download Now
White Paper - Trends in Industrial Filtration
Substantial progress has been made in filtration technologies in recent years. New filter media materials, designs and processes have led to filters that are more efficient, reliable, compact and longer lasting. This white paper will discuss the various trends that are impacting operational responsibilities of MROs today and the resources that are available for staying up-to-date on the latest filtration solutions. Download Now
Close Box
Join Eng-Tips® Today!
Join Us             Close