Tuning Fork type Level Switch installation

Tuning Fork type Level Switch installation

Tuning Fork type Level Switch installation

(OP)
Hello!

I have been reviewing some nozzle orientations for agitated vessels, and it has come to my notice that the nozzle for the level switch (tuning Fork type) is oriented adjacent to the pump recirculation inlet nozzle. Level switch installation guide recommends the switch should not be near any inlet nozzle.

How bad could be the implications of such an orientation? Is there anything that can be done to nullify them since the orientation has already been sent for fabrication?

Regards,
Piper
Replies continue below

Recommended for you

RE: Tuning Fork type Level Switch installation

I have used that type of sensor for solid bin level detection, never for liquid so that's outside my experience. However, if it's advised that it should not be near an entrance nozzle, that would suggest to me that it is affected by turbulence, which would prevail anywhere in an agitated vessel. I look forward to hearing other's input on this.

Brad Waybright

It's all okay as long as it's okay.

RE: Tuning Fork type Level Switch installation

A vortex breaker or similar at the entrance nozzle would help to cut out turbulence at the liquid surface if you have no other choice but to locate this tuning fork LT near this nozzle.

RE: Tuning Fork type Level Switch installation

The level measurement happens by the difference between frequencies of the tuning fork while vibrating in air and in water. If it is close to water inlet, you may get false indication as the water may continuously get poured on the tuning fork. You can try covering the fork in the direction of water flow.

RE: Tuning Fork type Level Switch installation

Doesn't the concern depend on whether you are trying to measure the level while you're filling? You can probably install a vane to block most of the turbulence, but a procedural change to allow the liquid to settle before taking an "official" measurement could also be possible.

TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! https://www.youtube.com/watch?v=BKorP55Aqvg
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers Entire Forum list http://www.eng-tips.com/forumlist.cfm

RE: Tuning Fork type Level Switch installation

Except IR, 3/4 of the time you use the level measurement to control the filling.

Keith Cress
kcress - http://www.flaminsystems.com

RE: Tuning Fork type Level Switch installation

Even had the tuning fork been installed correctly, any high flow filling operation would result in splashing and ripples, so there's a limit to its accuracy and some form of PID control would still be used for any accurate measurement of fill

TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! https://www.youtube.com/watch?v=BKorP55Aqvg
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers Entire Forum list http://www.eng-tips.com/forumlist.cfm

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close