Large quantities of rebar in isolated footing

Large quantities of rebar in isolated footing

Large quantities of rebar in isolated footing

(OP)
I'm fairly new to footing design, and I'm designing the column footings for a pre-engineered steel building. I have just finished calculating what would be needed for an interior column, using the procedure outlined in the "SE Structural Engineering Reference Manual" by Alan Williams. It takes an axial load of 83.47 kips, and I have determined it requires a 7.5' by 7' footing. The rebar required is much higher than I expected: I've got 11 #14 bars in the 7.5' direction and 10 #14s in the 7' direction. I've checked and re-checked my numbers, but that's what I'm coming up with. Does that seem reasonable to you folks?

As always, appreciate your time and effort.

RE: Large quantities of rebar in isolated footing

That does not seem right.

RE: Large quantities of rebar in isolated footing

Sounds high to me. That is a very low bearing pressure.

Looking at an old Reinforced Concrete Design Handbook, the lowest soil pressure considered was 2000 psf. For a column load of 100 kips, 12"x12" column, 7'-5"x7'-5"x14" footing the reinforcement recommended was 14-#5 each way.

BA

RE: Large quantities of rebar in isolated footing

Agree with Rabbit12.
How thick is the footing?

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: Large quantities of rebar in isolated footing

How thick is your 7.5' x 7' mat? Is there any uplift on this interior column?

Using 2000psf allowable bearing, I'm getting a quick and dirty bottom steel amount of 8's @ 12", for a d = 8" (running parallel to the 7.5' direction).

RE: Large quantities of rebar in isolated footing

(OP)
It's 2' thick. I'm using 1500 psf, which is what the Ohio Building Code specifies unless you do soil borings. Uplift is 13.79 kips.

RE: Large quantities of rebar in isolated footing

I get about (7)#5 which lines up with CRSI.

What are the column dimensions and foundation thickness?
Is the 83.47 kips a factored or service load?
Assuming service that load and foundation dimensions yields a bearing pressure of about 1.6 ksf is the allowable bearing 2.0 ksf?

Open Source Structural Applications: https://github.com/buddyd16/Structural-Engineering

RE: Large quantities of rebar in isolated footing

Are you using the 0.0033*(Ag) min or the 4/3*(Asreq'd) clause?

For footings, it typically makes a difference. (Temperature steel [0.0018*Ag] governs a lot of the time.)

RE: Large quantities of rebar in isolated footing

2' thick for that load you're probably going to be governed by minimum steel 0.0018*b*h = 0.0018*7.5ft * 12 in/ft * 2ft * 12 in/ft = 3.888 in2 or about (7)#7's edit: had ft/in instead of in/ft

Open Source Structural Applications: https://github.com/buddyd16/Structural-Engineering

RE: Large quantities of rebar in isolated footing

Thoughtclaw,

Using your numbers, it appears you footing is a touch small - 83.47 kips/ 1500psf = 55.65 sq.ft minimum. 7.5' x 7' = 52.5 sq.ft.

That being said, how are you calculating the moment in your slab? The way I learned was to apply the soil load to the footing, and treat the column point as fixed and design as a cantilever. Assuming 2000psf, and a LF = 1.6, you get (3.2ksf)*((7.5'/2)^2)/2 = 22.5 kip-ft / foot

Since the 83.47 is factored, moment becomes 11.2 kip-ft/ft - (4) #5's in the 7.5' direction.

And as Celt83 and WARose mentioned, minimum steel will likely govern.

RE: Large quantities of rebar in isolated footing

(OP)
That's a factored load. Can I ask what procedure you guys are using? I'm obviously doing something wrong here.

RE: Large quantities of rebar in isolated footing

(OP)
The moment equation I'm using is Mu=quL(B/2-c1/2)2/2

RE: Large quantities of rebar in isolated footing

Or you are calculating your moment over the full footing width, and not per foot width. Divide by the orthogonal footing width and you should be ok.

RE: Large quantities of rebar in isolated footing

Quote (Thoughtclaw)

The moment equation I'm using is Mu=quL(B/2-c1/2)2/2

Yep, that's the right formula. I just zero'd out the column/pier dimension for fast calculation, and did mine on a per foot basis.

qu = 83.47k/7.5'/7.0' = 1.59 ksf

L= 7'

B/2 = 7.5'/2 = 3.75'

Using the above formula nets me 78.3 kip*ft (with c = 0) = 939.1 kip*in

What are you getting for a moment?

RE: Large quantities of rebar in isolated footing

(OP)
Oh, I see what I did. I failed to do it on a per-foot basis. Well, I'm embarrassed! … But I'd rather be embarrassed and have the answer I need.

Thanks so much, everybody!

RE: Large quantities of rebar in isolated footing

If there are many of these footings, a soil report might save the owner a few bucks.

BA

RE: Large quantities of rebar in isolated footing

(OP)
The architect told the owner that, but I guess he figured he'd take his chances.

RE: Large quantities of rebar in isolated footing

Quote (Thoughtclaw)

The architect told the owner that, but I guess he figured he'd pay extra money for nothing

Fixed it for you.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: Large quantities of rebar in isolated footing

In my area, uplift tends to control footing weight more than gravity loads. I generally design interior columns for uplift first and then check gravity. I use working loads and my actual soil bearing under gravity loads tends to be 800 to 900 psf for interior columns. I do not know whether all loads you listed are factored or not but double check your FOS for uplift. I tend to use 1.5 for uplift.

If uplift is controlling footing size, soil bearing will be less of any issue on interior columns but may be more needed on exterior columns since they have overturning.

Isn't the 1500 allowed in your code an allowed and not factored value?

RE: Large quantities of rebar in isolated footing

(OP)
Thanks for mentioning that, Ron. I always check uplift, and it does often control. And yes, the 1500 is an unfactored value.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper - Understanding Critical Specifications for Dynamic Metrology Applications
Different types of metrology have different critical specifications to consider when determining which actuator technology to use. This white paper goes into detail on the demands of dynamic metrology applications as they apply to the selection of precision linear motion control components and systems. In addition, the relevance of Moore's Law is examined in the context of the industry. Download Now
White Paper - Permanent Non-Welded and Cold Bent Piping Solutions
Commonly used welded piping connections come with skilled labor, validation, inspection, and long commissioning times, as well as the workplace hazards associated with welding. Non-welded permanent mechanically attached fittings offer a viable alternative to welded piping systems that greatly reduces the time to commission piping systems through reductions in many of the time-consuming steps required in welding. Download Now
White Paper - Take Mobile Hydraulic Systems to a New Level
The introduction of digital ecosystems connecting electronic control hardware and software to the Cloud is catalyzing a new era of mobile machine and equipment design innovation. This is enabling OEMs across industries to develop customized solutions that digitally integrate hydraulic and machine controls with the Internet of Things (IoT). Download Now
White Paper - The Evolving Landscape of Commercial Battery-Powered Trucks
What’s driving the evolving landscape of truck electrification? What are the barriers, motivators and strategies for accelerating the electric transition? What insights and resources are available for today’s design engineers working to achieve industry disruption and evolution? For answers to these and other pertinent questions, read this white paper. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close