Chilled Water System Chemistry

Chilled Water System Chemistry

Chilled Water System Chemistry

(OP)
Not sure if this is the right forum, but here goes.

I have a chilled water system which uses an atmospheric storage tank, so I guess you'd call it "open-loop," although the system hardly loses or makes up any water at all.  I had a mild steel corrosion coupon in the system, which after a month, showed <.01 mil/year loss.  The way I understand it, the water is non-corrosive, and our water treatment program is working well.  Are there any conditions where I still could have active corrosion of the steel piping in the system, and it not show up on the coupon?  System circulation is good, so all the metal is seeing the same water.

---KenRad
Replies continue below

Recommended for you

RE: Chilled Water System Chemistry

Coupons are great to measure uniform corrosion. Local corrosion is more difficult to observe (MIC, pitting, intergarnular corrosion etc. One has to observe the sample under dimmed light (see ASTM G4), and still there is a possibility that it happens elsewhere. Can you tell a bit more about the water quality ?

Edwin Muller
KEMA Power Generation & Sustainables
Arnhem, The Netherlands
E-mail      e.f.muller@kema.nl
Internet: http://www.kema-water.nl


RE: Chilled Water System Chemistry

Any dissimilar metals in your system?

RE: Chilled Water System Chemistry

Like Edwin asked, what are your water parameters? I suggest a pH of 10.5-11.

Threaded connections are a likely spot and an easy place to check for corrosion.

I suggest hanging a piece of plastic sheeting inside your tank to act as a floating membrane to reduce CO2 and O2 absorption from the air.

RE: Chilled Water System Chemistry

Corrosion coupons are a good indicator of system protection if:
Coupons are representative of the system.  (This sounds like a no brainer but mistakes do happen.)

Coupons have been prepared properly.  They must be kept clean and not handled before insertion.  Body oils can provide a protective barrier from the solution.

RE: Chilled Water System Chemistry

KenRad,

The corrosion growth seems to be negligable.  At any rate,
we have two chiller plants.  I cannot recall off hand the condition of the piping or where the access fittings are installed.  However, I will post the operating conditions for you, any area of concern with regards to locations prone to corrosion growth and treatment measures. (dosing)


Cheers
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close