Minimum Foundation Wall Height above Grade Code confusion

Minimum Foundation Wall Height above Grade Code confusion

Minimum Foundation Wall Height above Grade Code confusion

(OP)
CRC 2016 R404.1.6 says minimum height above "finished grade" is 4" for masonry and 6" for concrete foundation walls.
CRC 2016 R317.1(5) says preservative treated wood siding, sheathing and wall framing on the exterior of a building is required when clearance is less than 6 inches from the ground or less than 2 inches measured vertically from concrete steps, porch slabs, patio slabs and similar horizontal surfaces exposed to the weather

R317.1 seems to indicate that the top of foundation can be minimum 2" above concrete and hardscapes. I can't think of any case where non p.t. wall framing and sheathing can be 2" from the ground therefore it seems these two codes are conflicting.

What is the code definition of "finished grade"? Does that mean soil surface or any surface including finished concrete?

RE: Minimum Foundation Wall Height above Grade Code confusion

In some areas there are wood-eating ants and other such bugs. They best need the earth right up to the siding. However, by having some clearance their open travel height ease of climbing is made more difficult. So above concrete it is in area where less ants may live, requiring less heights.

RE: Minimum Foundation Wall Height above Grade Code confusion

(OP)
I understand the termite concern but I'm questioning what is the code definition for "finished grade" because there seems to be a conflict in the two codes.

RE: Minimum Foundation Wall Height above Grade Code confusion

(OP)
anyone?

RE: Minimum Foundation Wall Height above Grade Code confusion

I'd think Finish grade is same as Grade, which is defined:
[RB] GRADE. The finished ground level adjoining the building at all exterior walls.
I'm only guessing, but think the R317.1(5) is not meant to apply to concrete block or concrete foundation tops, rather other wood items such as sheathing. E.G. are other foundation types allowed, such as All Weather Wood?

RE: Minimum Foundation Wall Height above Grade Code confusion

you usually place hardscapes, i.e. concrete patios, steps, etc. above finish grade therefore the two codes don't conflict.

RE: Minimum Foundation Wall Height above Grade Code confusion

(OP)
So concrete surfaces and other hardscapes are not considered finished grade? I just haven't seen an official definition of what finished grade is.

RE: Minimum Foundation Wall Height above Grade Code confusion

Finished grade is finished grade......whatever you step on......concrete, soil, alligators, etc

RE: Minimum Foundation Wall Height above Grade Code confusion

Finished grade from a design standpoint is what you step on.

But finished grade for this code is dirt, or final backfill material that's placed against the concrete foundation wall. As others stated, it's not concrete, asphalt, or other hard surface materials.

RE: Minimum Foundation Wall Height above Grade Code confusion

(OP)
But where does the code describe what they mean by finished grade? It's too unclear.

RE: Minimum Foundation Wall Height above Grade Code confusion

I hate it when sections contradict each other. I think it's generally accepted that finish grade is whatever surface you step on after construction is complete. BUT, exact word choice aside, I think the intention here for R404.1.6 is to have concrete or masonry foundation and retaining walls extend 4"/6" min above the adjacent DIRT, if there is any. I think "soil" would have been the better choice of words here than "finish grade". I would not consider this requirement to apply where the grade next to the wall is an impervious surface like concrete.

RE: Minimum Foundation Wall Height above Grade Code confusion

Finished grade means the surface of the ground after completion of final grading.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

eBook - Integrating the Engineering Ecosystem
Aras Innovator provides multiple options for integrating data between systems, depending on the scenario. Utilizing the right approach to meet specific business requirements is vital. These needs range from authoring tools, federating data from various and dissimilar databases, and triggering processes and workflows. Download Now
White Paper - Industry 4.0 and the Future of Engineering Education
With industries becoming more automated, more tech-driven and more complex, engineers need to keep their skills and knowledge up to date in order to stay on top of this wave—and to be prepared for the Industry 4.0 future. The University of Cincinnati offers two online Master of Engineering degree programs designed specifically for practicing engineers. Download Now
eBook - The Design Gridlock Manifesto
In this eBook, you’ll learn 6 ways old CAD technology slows your company down and hear how design teams have put those problems to rest. “The Design Gridlock Manifesto” shares first-hand modern CAD experiences from 15 companies around the world. Download Now
White Paper - Comparing Multi-Patterning at 5nm: SADP, SAQP, and SALELE
Self-aligned multi-patterning techniques such as SADP, SAQP, and SALELE are increasingly popular at advanced nodes, but each process has its pros and cons. IMEC and Mentor, a Siemens business collaborated to identify potentially less-obvious process and design limitations and trade-offs between the three SAMP techniques. Learn more in this paper. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close