Hello,

I have a question regarding catwalks at the rooftop. As per ASCE7-05, the uniform load is 40 psf and concentrated 300 lbs. Are these laods supposed to be applied together? I can't seem to find any text mentioning otherwise.

Thanks

RE: Rooftop Unit Equipment Load

IMHO, yes, apply the loads simultaneously.

My reason has nothing to do with the document's text, just engineering judgement:

If the catwalk is designed so "closely" that adding exactly one, 300 lb. concentrated load (anywhere on the catwalk) to a 40 psf UDL makes the structure "unsafe", the design is unrealistically "precise".

www.SlideRuleEra.net idea

RE: Rooftop Unit Equipment Load

(OP)
That's true. Thank You for the input.

RE: Rooftop Unit Equipment Load

In ASCE 7-10, 4.4 explicitly states it is either uniform OR concentrated, whichever produces the worst effect.

RE: Rooftop Unit Equipment Load

cgstrucg,

The Code does not require the UDL and the Concentrated loads to be applied concurrently. Essentially the UDS is for main carrying member design, and to provide sufficient mass in the building for the VFRS and the LFRS. The concentrated load often controls the grating design and the grating supports.

RE: Rooftop Unit Equipment Load

Long ago, my brother worked for a pacemaker manufacturer.
The pacemakers had a lead on them that the surgeon trimmed to length when installing it.
So as long as it was plenty long, it didn't really matter how long.
But, it was a highly regulated industry, so it had to be just so-so on paper.
So their slogan was "Measure it with a micrometer, mark it with a piece of chalk, cut it with a hatchet."
So, if I calculate seismic loads to 10 decimal places, that's the thinking behind it.
On the loads there- yes, see 4.4 and also note that it defines how big a "concentrated" load is. Also, see the load combinations in Chapter 2.
OSHA has some load requirements for stairs and ladders, but I don't see anything specific for general walking surfaces.

RE: Rooftop Unit Equipment Load

Cgstrucg:
The 300lb. concentrated load is sorta supposed to represent a 250lb. worker and 50lbs. of tools and equipment, per OSHA and others. Then, I wonder if you’ve ever seen two guys working close together on something, plus a few pieces of pipe or other bldg. material laying on the catwalk? I’m inclined to agree with SRE and also agree with jittles thinking, ‘which ever produces the worst loading.’

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources

Ebook - Mastering Tolerances for Machined Parts
When making CNC machined parts, mastering tolerances can be challenging. Are general tolerances good enough? When does it make sense to call out for tighter tolerances? Do you need a better understanding of fits, datums, or GD&T? Learn about these topics and more in Xometry's new e-book. Download Now
eBook – How to Choose the Correct Corrosion Testing Method
When designing a metal component, engineers have to consider how susceptible certain alloys are to corrosion in the final product’s operating environment. In a recent study by NACE (National Association of Corrosion Engineers), it was estimated that the direct and indirect costs of corrosion in the United States is approximately 6.2% of the GDP. In 2016, that cost exceeded $1 trillion dollars for the first time. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close