ASCE 113 Update

ASCE 113 Update

(OP)
Hello transmissiontowers, I was just checking in to see if we might get an updated ASCE 113 this year.

I copied a reply from an old thread below since they closed it:

We have a meeting in Feb 2018 to look over committee comments and after that we have a spot on the agenda of the ETS conference in November to give a status update at the pre-conference. After that we will send to peer review and then address the peer comments we get back. Probably sometime in 2019 to go to publication. Lots of loose ends to fix. I know ASCE has been after us to finish, but getting 25 Structural Engineers from all over the country to agree to technical details is like hearding cats.

Thanks!

RE: ASCE 113 Update

joshab, I actually just asked him about this on May 9th in this thread: thread593-445268: Transmission Tower Anchors
His response was,

Quote (transmissiontowers (Structural))

We are meeting next week to talk about it. Hopefully we will make some progress, but don't hold your breath. We still have to get it where all committee members agree and then on to peer review and address comments.

RE: ASCE 113 Update

(OP)
Glad I didn't start holding my breath last time either!

RE: ASCE 113 Update

I am Chair of the ASCE 113 revision committee. I don't get around to posting here very often since they reorganized the sections. We are getting closer and have a meeting scheduled for mid-November. Most of the issues have been argued to death and we still lack a examples section of worked examples. This meeting is supposed to be our last and it's good to have goals. :)

_____________________________________
I have been called "A storehouse of worthless information" many times.

RE: ASCE 113 Update

A quick update. We are getting closer to finishing the revision to ASCE 113 for those that asked. We had a meeting in Houston in mid November 2019 and have started to wrap up with Skype meetings of a smaller editorial committee to put the chapters together. Then we go to peer review, and make changes as requested. Then onto publication.

_____________________________________
I have been called "A storehouse of worthless information" many times.

RE: ASCE 113 Update

(OP)
Thanks for the update. Very curious to see if there will be an update to load combinations which address compatibility with wind speeds specified in ASCE 7-10 and later.

RE: ASCE 113 Update

transmissiontowers, is the peer review that you refer to the public comment period that ASCE standards go through or is it something else? Or to ask my question in a different way, will the new version go through public comment or is that only required/done for full blown standards?

RE: ASCE 113 Update

I don't get by this forum often enough. I'm not sure why I do not get eMail notifications for this thread.

We had our Houston meeting and are trying to speed things along. To joshab; We have gone to ASCE 7-16 wind maps and have a couple of tables for load combinations. We have one for LRFD load combos and another for ASD loads. We recommend LRFD for most structures, but recognize ASD should be used for deflection cases and probably for foundation design. Deflection cases are done for less than extreme wind loads (if you want). Of course, you can check deflection at 140 mph if you want to, but realistically you probably want to check for winds where the equipment might be expected to operate like a disconnect switch. We have greatly expanded SCF equations and given the option for doing a full dynamic analysis (if you have the time and data) of a SCF case with forcing functions. Normally, we just use IEEE 605 type equations and use the max static load and combine with extreme wind or extreme ice. The simple steady state equation is given for those that wish to use it. The left coast guys have expanded the seismic equations and you have the option to do a full dynamic analysis of seismic cases. One key point is that even though we give load combinations and suggested factors, you do not have to consider every load. You probably do not need to combine a hurricane wind with SCF and a seismic load with an ice storm and do a full dynamic ANSYS run to find the force in a beam or column. Anchor bolt design has been revised for the case where the base plate is on leveling nuts.

To dauwerda; Once the committee has edited the chapters, we will select a few people to do a peer review and combine all the chapters into one PDF. Since we are still a Manual of Practice, there is no public comment phase. Once the peer reviewers return their review comments and suggest changes if any, we will vote as a committee for each change and if it should be done or not. The first edition of 113 had over 1000 comments and changes requested. Many were just grammatical, and some were substantial and we adopted most but not all.

One thing that we are trying to include is an Appendix for a Proposed Draft Pre-Standard of what 113 might look like if it were to become a Standard. I believe ASCE 74 did the same. The Appendix is just to get comments from users on how they like or dislike it.

_____________________________________
I have been called "A storehouse of worthless information" many times.

RE: ASCE 113 Update

(OP)
Will the LRFD wind load factor match the ASCE 7 factor (1.0) or will it be something less like in the current version of ASCE 113 such as (1.2/1.6) ?

RE: ASCE 113 Update

I found out that my Gmail had classified Eng-Tips as Span and notifications were in my Spam folder, so that is why I am late in responding to these threads.

I'll logon to my work PC and look into the factor question since I don't remember off the top of my head, but in general when you compare 113 or 74 or other T-Line ASCE documents, we generally do not have the loss of human life as a factor in our documents. ASCE 7 has to consider the building or bridge as a potential loss of life category. A substation structure or T-Line tower is less critical than a building and we use lower factors. There is a lot of research behind the wind and ice maps in ASCE 7 but they sometimes include factors that the T-Line industry does not use.

Electricity is becoming more important as technology depends on it and we may get to a point where regulators dictate that we use bigger factors to prevent wide blackouts. All it will take is for some US Senator's child not to be able to post a picture of their latest meal on Facebook or Insta-Whatever in a blackout, and we will be designing structures for a 3000 year return period wind storm that coincides with a 7000 year return period earthquake and a Short Circuit event with 3 inches of radial ice. bigsmile

_____________________________________
I have been called "A storehouse of worthless information" many times.

RE: ASCE 113 Update

Here is a snip of the load combination table for LRFD or USD design from the proposed new guide (the subscripts like "a" and 300 and 100 did not come over ie. 1a means case 1 with a note a that means the Owner should determine if you need to combine SC with the other loads in the Case):




Table 3-18 Ultimate Strength Design (USD) Load Combinations


CASE COMBINATIONS (all 8 cases may not apply)
1a 1.1 D+1.0 W_300+0.75 SC+1.1 T_(WI-300)
2a 1.1 D+1.0 I_100+1.0 W_(WI-100)+0.75 SC+1.1 T_(WI-100)
3 1.1 D+1.0 SC+1.1 T_APP
4a 1.1 D+1.0 E+0.75 SC+1.1 T_EA
5a 0.9 D+1.0 W_300+0.75 SC+1.1 T_(WI-300)
6a 0.9 D+1.0 I_100+1.0 W_(WI-100)+0.75 SC+1.1 T_(WI-100)
7 0.9 D+1.0 SC+1.1 T_APP
8a 0.9 D+1.0 E+0.75 SC+1.1 T_EA

a The combination of SC loads with extreme events listed above should be determined by The Owner

Table 3-18 and Table 3-19 show suggested design load cases, combinations, and minimum load factors to be use for substation structures. For the load conditions that include ice, the effect of icing on the wire dead load and wind load concurrent with the ice formation should be included. The individual load components are the following:
D = Structure and equipment dead load;
W_300 = Extreme wind load (F, from Equation 3-1,) from 300yr MRI wind map;
I_100 = Extreme ice load from 100yr MRI Ice Map;
W_(WI-100) = Concurrent Wind load in combination with ice from the 100yr MRI ice map;
T_(WI-100) = wire tension resulting from the following loads acting simultaneously: weight of the wire; weight of ice corresponding to ice thickness in the 100yr MRI ice map; wind load on the iced wire corresponding to wind speed in the 100 MRI ice map and: wire temperature per Figure 3-3a through Figure 3-3e.
E = Seismic load as defined in Section 3.1.7.8;
T_(W-300)= wire tension due to wire weight acting simultaneously with the wind force corresponding to the wind speed from the 300yr MRI wind map at an ambient temperature determined by the Substation Owner;
SC = short circuit load;
T_APP = wire tension due to the wire weight acting simultaneously with any appropriate ice weight and temperature as determined by the Substation Owner (every day or normal operational conditions);
• T_EA= wire tension corresponding to wire dead load acting simultaneously with the seismic loading per Section 3.1.7.13, at an ambient temperature determined by the Substation Owner


The above text is very preliminary and subject to peer review and could change before it gets published but it is the current thinking of the Committee.

_____________________________________
I have been called "A storehouse of worthless information" many times.

RE: ASCE 113 Update

Thanks for the above information transmissiontowers, any chance we can get an update on the progress or a targeted publication month?

RE: ASCE 113 Update

Working from home has been tough to get things going. We have been doing weekly 1 hour Zoom/Webex meetings between an editorial committee of about 6 folks. We are getting closer but still need to address the Appendix for the Draft Pre-Standard section. I hear ASCE 74 had one that was a "What-If" this MOP were to become a Standard to generate comments. The Examples also need some work. We are about to select the Peer Review committee and then will have to address all the Peer comments. IIRC, the 1st Edition had over 1000 comments that had to be addressed (I was Vice-Chair for the 1st edition)
Hopefully, sometime in 2020 will get it to ASCE.

_____________________________________
I have been called "A storehouse of worthless information" many times.

RE: ASCE 113 Update

Hello transmissiontowers, thank you very much for the hard work and the updates!

I am currently reading ASCE 74-20, and well, many things change, I think for the good.

We are now reaching the end of 2020. Any news on the process for ASCE 113?

RE: ASCE 113 Update

The ASCE definitely wants us to finish up soon and we are in the final stages of an Editorial Committee review of the chapters. The Peer Reviewers have been chosen and I told ASCE I would try to get a document to the Peer Reviewers by 1-31-2021.

I have gotten a PDF of ASCE 74 but have not gotten around to reading over it yet. IIRC, their wind maps are the same as 113's but the big change for my part of Texas is the hurricane prone regions are now in Exposure D according to ASCE 7-16 (we used to be in Exp C)

My other observation is the NESC-C2 that covers all things on T-Lines, still uses the wind maps from ASCE 7-05 and the NESC is very slow to change. The dilemma is, do I abide by NESC (not a design code, but a public safety code) or do I use MoP 74 and their wind maps?

I have a friend in Louisiana that was asked what the cost impact would be to design poles and towers for a 170 mph wind vs the 140 mph wind in the NESC (about a 50% increase in loads) because all the T-Lines went down in the hurricanes that hit them this season.

_____________________________________
I have been called "A storehouse of worthless information" many times.

RE: ASCE 113 Update

My instinct would be to follow ASCE 74 and/or ASCE 7-16... Following NESC now is so out of date, and as you stated, just a safety code, not code. I think using a 200-year MRI would be reasonable for ultimate design, alone with a 25 yr MRI for deflection. Thanks @Transmissiontowers for keeping us posted! It's sad that it excites me to know an updated ASCE 113 is coming out... Please tell me their will be some new info on foundations and anchors (specially drilled piers)!

RE: ASCE 113 Update

Hi StructureME;
The owner of the T-Line or Substation decides which codes to follow with input from the engineers. Historically the NESC with OLF's >1 on Rule 250C wind maps has served well in my Utility with few T-Line and Substation structure failures during hurricane events. IIRC, there is an exemption in 7-16 for electric utilities because we do have NESC and ASCE 74 to use for wind maps. Electric power is becoming a "can't do without" commodity and might get the attention of the regulators that could force us to be a Risk Category IV for new designs.

AFA the foundation, yes we will have a chapter on them but it is very generic to say what are the general types of foundations in a Sub. There are no equations in the chapter for what the capacity of a foundation is. We do have load combination tables to use with the foundation that are based on ASD. I do not do foundations myself and have always used a USD approach for the steel design, so designing foundations is very foreign to me. As long as you tell the Geotech the reactions and the OLF's that are included in them, they should be able to come up with a foundation that will withstand the ultimate loads.

On the anchor "rods", there is a new method based on a European ETAG code but the big change is for the base plate on levelling nuts, you will always have to include the bending moment in the bolt. ASCE 48 allows you to neglect the bending if the the gap is less than 2 bolt diameters, but 113 recommends to always use the bending, no matter the gap.

HTH

_____________________________________
I have been called "A storehouse of worthless information" many times.

RE: ASCE 113 Update

I looked over my old eMails and came across this statement I put together for one of my many bosses:


The ASCE 7-16 applies to buildings and other inhabited structures. NESC C2-2017 recognizes that transmission lines, distribution lines, and substation structures are uninhabited in extreme events. ASCE 7-16 has a section in the previous edition ASCE 7-10 on Page 506, Section C26.1.2 Wind, where the electric utility industry has an exemption from the wind maps. I believe it is because we have developed a loading guide, ASCE 74, that applies to our structures plus the NESC.

These are my opinions and may not hold up in court. :) bigsmile

_____________________________________
I have been called "A storehouse of worthless information" many times.

RE: ASCE 113 Update

Again, that is for all the info and insight, Transmissiontowers! I would love it if you were correct and the industry segregated from ASCE 7 and just used its own wind loading. Far too often than not, I have a client who's standards use ASCE 7-05, State building code uses 7-10, and NESC also needs to be considered - end up having hundreds of load combinations! As for foundations and anchors, ACI 318 is the industry standard, but fails to discuss anchors in drilled piers well, which are used all the time in our industry! That's really why I was hoping it would be addressed, but I guess we'll just continue as we've been doing it.

Thanks again!

RE: ASCE 113 Update

StructureME, as far as designing anchors (and their supplementary reinforcement) in drilled piers are concerned one of the main references I have seen used (perhaps "adapted" would be a better term) is, "Design of Anchor Reinforcement in Concrete Pedestals" by Widianto. It can be downloaded here:
https://www.semanticscholar.org/paper/Design-of-An...

Another resource is ASCE's "Anchorage Design for Petrochemical Facilities"
https://ascelibrary.org/doi/book/10.1061/978078441...

Unfortunately these do not address round piers, but I believe engineering judgement can be use to apply the same principals.

RE: ASCE 113 Update

Dauwerda - I've used those, specifically the strut and tie paper you linked. They are useful, but I suppose the question remains how to treat round ties as supplemental shear reinforcement. IMO, the shear ties confine the concrete cone from breaking out, but I still haven't found a good reference on exactly how much of the time can be considered "developed" since it's round. This is something heavily debated in our structural department, so other opinions are graciously appreciated!

I'm new to eng-tips, so sorry if this is now digressing from the original post.

RE: ASCE 113 Update

StructureME;
I don't do foundation design (I always tell people I proudly put my mistakes up in the air for all to see as opposed to the foundation people who bury their mistakes) and am unfamiliar with 318 but I gather you are trying to size the hoops or spirals or ties for the shear reinforcement of the drilled pier. The 1st edition of 113 (I was Vice-Chair on that one) in section 7.3.3 and Figure 7-6 talks about ACI 318 and the development length of the vertical rebar and the use of smooth and deformed bar anchor bolts and how much development length you need.

On the ASCE 7-16 question, point your clients to the part that exempts T-Lines and let them know IEEE C2 is a national standard with maps done for our industry plus the new edition of ASCE 74 which uses maps from 7-16. For substations, 113 is just a MOP but we do use the maps from 7-05 for the 1st edition and the 2nd edition coming out will use 7-16 maps.

Early next year we will install a big 220' T-Line pole with 100 #18 anchor bolts in a double cage, 15'-0 diameter drilled pier (14'-0 diameter cage of #18 rebar), 60'-0 deep. IIRC, the ties are #6's and I think they are 4" spacing where the anchor bolts are up in the cage. The contractor says they can drill a 16'-0 hole 100 feet deep if we need that much of a foundation.

_____________________________________
I have been called "A storehouse of worthless information" many times.

RE: ASCE 113 Update

Transmissiontowers, that's actually another debated opinion in our group; the exemption in ASCE for transmission and whether or not it applies to substation structures and foundations. I believe the exemption does apply for wire supporting tline towers, but not necessarily heavy 1million lb transformers on foundations, control buildings, or switch stands inside the yard. I think for now, until the newer ASCE 113 comes out, we'll likely stick with whatever building code governs the state, and NESC for wire supporting structures that tie into our substations just outside the fence. If the state uses a building code corresponding to ASCE 7-05, I think it's appropriate to use ASCE 113.

And holy cr*p that's a big foundation! Must have massive tensions on those wires!

RE: ASCE 113 Update

I get your point on the NESC inside the fence. The new 113 was very careful not to use the term "building" when describing that function and started using Control Enclosure to describe the spot in the yard where the control cables are located. We did not want to have a local building official require ADA ramps and bathrooms inside our substation fence. We did not want to get into the structural design of the Control Enclosure.

This is the statement we now have:
"Control enclosures contain the switchboard panels, relaying and controls, batteries, battery chargers and other equipment for metering and communications. Control enclosures may be designed by the supplier as part of the equipment contained within, or by using rules similar to non-building structures. Control enclosures are not covered in this document."

We are also working on an Appendix (like the one in ASCE 74)as a Pre-Draft Standard for what the MOP would possibly look like if it were advanced to an ASCE Standard and to gather comments from users. A few years after the 2nd edition of 113 comes out, the next step would be a new committee to create the ASCE Substation Structures Design Standard XX, which would have the wind, ice, and seismic maps and all the design equations or point to the document where they are located like the AISC Manual.

The big pole is a 30° double circuit vertical 345 crossing over a road or another 138 circuit. Three 959 ACSS wires per phase with a full dead end capability on both circuits so we terminate 18 wires with a RBS of about 33 kips each plus a couple of OPGW wires. bigsmile

_____________________________________
I have been called "A storehouse of worthless information" many times.

RE: ASCE 113 Update

(OP)
Hello transmissiontowers,

Any chance the updated version of ASCE 113 has made it to peer review?

RE: ASCE 113 Update

We are getting closer but have not sent it to peer review yet. All chapters are mostly done with some grammar checking to finalize. The big hurtle will be the examples Appendix which has been worked on but needs to be put into DOCX format from Mathcad. The ASCE publishers want all equations in Word Equation Editor and most of the chapters are already done but a few remain. Once all the Chapters are done, we need to work on the Appendix for the Pre-Draft Standard. The initial thought was to wait a few years to get comments on the Standard idea and then start on it. The thought now is as soon as the 2nd edition is published, a new Committee will be formed to tackle making 113 into a Standard.

One friend on the committee attended a Webex on ASCE 7-2022 and there will be a new section on Tornado Loading on buildings and other structures in 2022. Basically from El Paso to the tip of Maine will have to consider Tornado loads. The though process is, if we have a Loading Standard for T-Lines (ASCE 74 as a Standard) and ASCE 113 as a Standard for substation loads and design, we can fight off the Building guys that want us to use ASCE 7-22.

I have tried to point out when the bean counters come around to try to reduce substation costs, that reducing the cost of substation structures by reducing overload factors is not very safe and not cost effective. If the cost of the steel in the substation was free, the overall cost of the land and wire and equipment combined would still be 85 to 90% of the total substation cost. The labor to build the substation would still be there. Talk to the provider of the 2 million pound auto-transformer and negotiate a 10% cost reduction if you want to save money.

I had one EE manager come ask me if I could remove all the lacing in the bottom 20' of all the lattice towers to prevent people from climbing them. Obviously the EE's did not study L/r. I told him we could if he did not mind the tower line falling over in a 10 MPH wind. The tangents might stand up for a while but the angle towers and dead ends would fall over as soon as the last bolt was removed. :)

Sorry for the long and rambling answer, but I've been working from home for almost a year in my home office.

_____________________________________
I have been called "A storehouse of worthless information" many times.

RE: ASCE 113 Update

@transmissiontowers,
Thanks for the update, I completely agree with cutting substation costs! Stop complaining about using a W12 column when the circuit breakers cost 10X the value!! I just got done analyzing a huge lattice structure in California, only to hear the client complain "well it's been standing 50 years so I disagree with your assessment of member failures!" Unfortunately, it's hard to talk to a non-structural person about wind MRI's and single angle compression...

Side question: how can one join ASCE 113 committee?

RE: ASCE 113 Update

The bane of the structural engineer is every kid that ever built a tree house (do they still do that?). Sure, you can come up with anecdotal evidence that this or that structure has been around for 30 years so if we add double the wind load and triple the weight, it should be fine.

You can build a simple structure that will stand up when there is no wind, but we have to deal with a 100 year event. I had a friend build a metal storage shed in his backyard. He had the walls up when a wind came and he was chasing it around the yard and it was almost destroyed before he could attach it to the bottom and get the roof on it.

One telecom guy wanted to put a MW Dish on a concrete pole mounted at 85'-0 AGL so he said he needed a 85'-0 tall pole. I told him he would need at least a 100' long pole and maybe more depending on the soil and the size of the dish. He says, well it only weighs 150 pounds, so any old pole would work. I told him that if he wanted it to stand up to a 10 mph wind, maybe any old pole would work, but in a 140 mph hurricane wind, a bigger pole would have to be used because you are putting a big sail on top of a flexible pole and the dish may not be pointing at the target when the hurricane blows in. What good is a MW Dish that looses communication when the wind blows over 40 mph?

Off my soap box. :)

The Current ASCE 113 committee is wrapping up, so no new members are being accepted. When it is published, there will be a new effort to move it to a Standard like ASCE 48 or ASCE 10. The just published ASCE 74, is moving to be a Standard and you can inquire about getting in on that effort. The original thought was that ASCE 74, 4th Edition (which has a Draft Pre-Standard Appendix) would be left out in the public to gather comments and in a few years, it would be ready to be elevated to a Standard. The current thinking is to go to the Standard soon to stave off the calls for us to abide by ASCE 7 loading. T-Lines are not buildings where loss of human life has to be considered, although in my part of Texas several people died last week trying to stay warm without electricity. Mostly from carbon monoxide using charcoal grills inside the house or a gasoline generator inside the garage.

When 113 is done, ASCE will want a new Committee to advance 113 to be a Standard. Just changing a few could's to shall's will not be enough. It will be a huge effort and I will suggest that they get an expert in MS Word to help with the effort. I am learning more about Word and Tracking Changes but citing references and keeping track of section 6.3.1.2.7.3 when it was moved and adding 3 equations before Equation (6-4) and renumbering everything between (6-4) and (6-42) and finding the places in other Chapters that refer to the old Equation 6-41 that became Equation 6-44 is a giant task. For those that have read this far, look up the free Agent Ransack program that searches Word DOCX files in multiple folders for text so you can see where Section 6.3.1 is called out.

Another Word Tip. Copy your DOCX file and rename it with a ZIP extension and look inside the ZIP file to find the pictures and figures that are JPG, PNG, or TIF if you lost the original file that was inserted.

_____________________________________
I have been called "A storehouse of worthless information" many times.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close