Just wondering what you all do in practice, and what your seismic loads are like. Most of my searches online come up with the assumption that the top plates are the collectors. This doesn't make much sense to me, and except for extremely low demand collectors I can't think of even one reason to use the top plates.
(1) the rim joist is closer to the plane of the diaphragm
(2) the rim joist is nailed directly to the diaphragm
(3) the rim joist is inline with any roof beams over full height openings where the double top plate is non-existent
(4) the rim joist is has fewer splices and is easier to splice (just strap over the diaphragm or on the side where shear wall nails are not required).
This last point may not be true in very low load collectors under a couple kips, where a double top plate with 20 splice nails might be sufficient. Also, if the rim joist is the collector, we need clips both sides @8" to handle the shear in moderate to highly loaded walls with the 1.25 multiplier per ASCE 7-10, 12.3.3.4 (SDC D-F, certain common irregularities (including diaphragm discontinuity and reentrant corners)).
Most of my jobs are SDC C, D, or E.