Post-installed concrete screw anchor: ICC-ES approval
I am designing a post-installed concrete screw anchor as per ACI 318-11. This particular screw anchor is not approved by ICC-ES (International Code Council- Evaluation Service).
Is it mandatory to use ICC-ES approved anchors when ACI 318 is the governing code?
Su
RE: Post-installed concrete screw anchor: ICC-ES approval
ACI 311-18 doesn't require the use of ICC-ES approved anchors. However, Appendix D does have limitations on anchor diameter. The purpose of the ICC-ES report is to show the anchor does or doesn't do what the manufacturer claims.
Thank you bridgebuster!
Su
you're welcome