Deflection in a 12" sch 40 pipe (with internal pipe supports) problem
I have to find out deflection in a 12" pipe with fixed bearing supports at both ends. However, the ID of this pipe has an internal smaller pipe with equally spaced 1" wide rings (donuts) plug welded in place for better support internally. My question is, how do I calculate deflection of the entire assy? Would I have to neglect the welds?
Bill H.
RE: Deflection in a 12" sch 40 pipe (with internal pipe supports) problem
If the welding is sufficient, you may have the two pipes working together, in which a larger I would be warranted. You would have to do a shear flow analysis.
Do you have a model of what you describe that you can post?
Mike McCann, PE, SE (WA)
Are the internal centering rings tight to both pipes?
If not then they don't matter.
By the same token if they are far apart they may not add a significant amount of stiffness either.
Quote (BILL486)
Before making a judgement call on the effect of the internals, find deflection upper and lower bounds:
1) Calculate defection ignoring the internals.
2) Calculate defection assuming the internals contribute 100%.
If the internal pipe is "small" (giving it a relatively low moment of inertia) compared to the 12" pipe, upper and lower deflection bounds will probably be surprising close together... making the judgement call much easier or not even necessary.
www.SlideRuleEra.net idea
I like SRE's advice on the upper/lower bound check - I find myself sweating over decisions sometimes and once you run the numbers you realize there wasn't much a choice to make anyway.
Aside from that - if the pipes are centered on each other, there is no shear flow - Q = 0 and then so does VQ/IT. In that case, the composite section would have the same stiffness as the non-composite section. I believe there was a fairly extensive thread on this topic a few months back.
Attached is a diagram of the question.
Yeah, add the stiffness of the inner and outer tubes but expect the outer tube's contribution to domiinate.
Can I ask what this installation is trying to accomplish?
I would only consider the outer pipe. I don't think those "donuts" will be able to transfer the horizontal shear required for the section to act compositely unless they are very thick or stiffened.
In any case, the major contribution to resistance would have come from the outer pipe, anyways.
Quote (Michael Chen)
Both individual pipes and the composite section all share the same centroid - shear flow is zero.
Not sure how big the inner pipe is, but a 12" pipe has an I=262 in^4 and for example if the inner pipe is 4" its I=6.82 in^4. If it is a composite section it is not really much bang for your buck. The two pipes are concentric, so the combined I is just the sum of the two individual I's.
I would probably just look at the outer pipe and be done with it.
Click Here to join Eng-Tips and talk with other members! Already a Member? Login
White Paper - Implementing a Multi-Domain System
IoT systems are multi-domain designs that often require AMS, Digital, RF, photonics and MEMS elements within the system. Tanner EDA provides an integrated, top-down design flow for IoT design that supports all these design domains. Learn more about key solutions that the Tanner design flow offers for successful IoT system design and verification. Download Now