Sizing Carpark Exhaust Shaft

Sizing Carpark Exhaust Shaft

Sizing Carpark Exhaust Shaft

(OP)
Hi guys.

I am currently doing design on Carpark Ventilation, the building has 6 basement Carpark floors.
Can I consider a diversity at the shaft's total airflow in sizing the shaft itself?if yes, how much diversity can I use?
what maximum velocity can I consider in sizing the shaft?

RE: Sizing Carpark Exhaust Shaft

Hi Ogsray,

Is there possibility to fill all 6 basement carpark floors at a time? If it is so, diversity does not work to size shafts. I think shaft is sized according to the max air flow rate and you can put more than one fan with frequency drive. Therefore, you can fulfill the full air flow condition at max condition and with frequency fans, you can arrange air flow rate with respect to the part load condition. Please also check which one is critical smoke exhaust flow rate or normal exhaust flow rate.

Regards,
Emre

RE: Sizing Carpark Exhaust Shaft

(OP)
Hi Emre,

Thanks for the reply and I agree with you on the"I think shaft is sized according to the max air flow rate".
Basically I am having 4 exhaust risers connected with 1 axial fan each riser and each floor. And I am coming up with a velocity at shaft of 12m/s considering maximum airflow. Is this velocity too much? What velocity can I use?
For the Smoke Control at Carpark, what standard can I look into for the rate(ACH)?

Thanks

RE: Sizing Carpark Exhaust Shaft

Ventilation rate is given as roughly 7.5L/s-m2 for parking garages according to Table E-2 from ASHRAE Standard 62-2001 Addendum n. (please note that exhaust not required if two or more sides comprise walls that are least 50% open to the outside) However, It is 300L/min for min. according to NFPA 88A. For more accurate calculation if needed, you need to have the number of cars in operation and the emission quantites. (i think you can decrease investment cost by making detail calculation since standard values give more than necessary)
For your interest: https://www.academia.edu/28614713/Ventilation_for_...
I think velocity is optimum at 10-12 m/s for normal condition and 15m-18m/s for smoke exhaust condition.
You can look into NFPA standards for smoke control at carpark.
Regards,
Emre

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper – Data Security and Know-How Protection
Our data is constantly exposed to the danger of being intercepted or stolen as it wends its way over global data networks. Data security measures and measures for protecting intellectual property should not, however, first be implemented when data is exchanged – companies must lay the foundation for these measures within their own organization. Download Now
White Paper – Collaboration in the PLM Context
The influence exerted by the Internet of Things (IoT) means that there is a steadily growing need for collaboration in industry. Partners from new industries and areas of application need to be integrated in cross-company business processes to ensure that the lifecycle of smart, connected products can be managed from end to end. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close