Hello all,
I am doing off design performance prediction of steam turbine at different load. But I am unable to predict the two main key parameters i.e isentropic efficiency and outlet pressure. I have used stodla elliptical correlation but it doesn't fit good with the given HMBD of steam turbine manufacturer.
Turbine detail :
60MW extraction cum condensing turbine with two HP heater, 1 deaerator, 2 LP heaters and one condenser
Can any one suggest any excel sheet or pdf doc. Which will be helpful for me during calculation.
I am doing off design performance prediction of steam turbine at different load. But I am unable to predict the two main key parameters i.e isentropic efficiency and outlet pressure. I have used stodla elliptical correlation but it doesn't fit good with the given HMBD of steam turbine manufacturer.
Turbine detail :
60MW extraction cum condensing turbine with two HP heater, 1 deaerator, 2 LP heaters and one condenser
Can any one suggest any excel sheet or pdf doc. Which will be helpful for me during calculation.
RE: Steam turbine off design performance prediction
Have you read their (original) tech manuals for the steam conditions at each stage extraction and condenser temperature at 100% power?
With that information at each stage at 100% power (or from the plant's MEASUREMENTS at 100%, 90%, 80% power, run it for an hour just before shutdown at 50% and 60%.
RE: Steam turbine off design performance prediction
However, if you have the manufacturer's Heat and Mass Balances at part loads you may be able to plot various parameters like isentropic efficiency vs throttle flow so you can calculate performance at part loads. Once you have these plots, you may be able to develop an Excel spreadsheet to assist with calculations. Even then, you will have to iterate calculations for various components to get agreement between components.
Best of luck!
RE: Steam turbine off design performance prediction
The exhaust pressure is not predictable unless you know the condenser sizing and circulating water temperature, whihc is a function of the ambient air temperature and the wet cooling tower size or ACC performance parameters.
The part load performance is also dependent on the turbine inlet valve position ( constant pressure or variable pressure) and the iinlet steam temperatures ( which vary as load drops , depending on boiler characteristics).
At very low load ( < 15% MCR hot reheat steam flow) there can be extra losses at the L-1 exhaust blades due to "recirculation" or aerodynnamic instability.
All of the above considerations are usually modeled in the canned programs.