ACI 318-14 Sect 22.9.4 - Nominal Shear Strength

ACI 318-14 Sect 22.9.4 - Nominal Shear Strength

ACI 318-14 Sect 22.9.4 - Nominal Shear Strength

(OP)
Does this section apply to cases where concrete is poured against concrete without any reinforcing across the joint? Say, a slab poured against a concrete retaining wall? That is a shear plane, and I'd like to considered the ability for this plane to transfer load.

RE: ACI 318-14 Sect 22.9.4 - Nominal Shear Strength

No - it only applies where you have reinforcement across the joint as stated in 22.9.4.1.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: ACI 318-14 Sect 22.9.4 - Nominal Shear Strength

(OP)
That section in my ACI copy, 318-14, just says "Value of Vn accross the assumed shear plane shall be calculated in accordance with 22.9.4.2 or 22.9.4.3. Vn shall not exceed the value calculated in accordance with 22.9.4.4"

It mentions minimum shear-friction reinforcement areas, but doesn't say anything about shear across unreinforced areas. I suppose this value is normally ignored. In my case, I have a slab at the bottom of a hole with concrete walls. I would like to count on some unreinforced friction to resist the possibility of small uplift forces.

RE: ACI 318-14 Sect 22.9.4 - Nominal Shear Strength

Section 22.9.4.1 references the two other sections that explicitly define the amount of shear you can estimate based on reinforcement areas. There's limits on those two values based on concrete area but there is no shear friction where you don't have reinforcement per ACI and this section.

Concrete shrinks so a slab "against" a wall may not really be tight to it for the long term.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: ACI 318-14 Sect 22.9.4 - Nominal Shear Strength

(OP)
Ok, fair enough. Makes sense to me, thanks!

RE: ACI 318-14 Sect 22.9.4 - Nominal Shear Strength

Quote (hemiv)

I would like to count on some unreinforced friction to resist the possibility of small uplift forces.

If the retaining walls push into the slab such that you had reliable compression in the slab under uplift, you could use that compression in place of the clamping reinforcement required by ACI. Estimating the reliable compression in this case would be a pretty difficult task, however, so I'd be inclined to find another solution. Chances are that you're dealing with a four sided shaft where the walls may be spanning horizontally rather than vertically anyhow.

Is the slab existing?

RE: ACI 318-14 Sect 22.9.4 - Nominal Shear Strength

(OP)
No, slab is not existing. Circular shaft with secant pile walls. I'm going with dowels to the wall at this point. Although it would be nice to count on friction, I think JAE is right about shrinkage.

RE: ACI 318-14 Sect 22.9.4 - Nominal Shear Strength

Oh yeah, dowels all the way.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

eBook - Integrating the Engineering Ecosystem
Aras Innovator provides multiple options for integrating data between systems, depending on the scenario. Utilizing the right approach to meet specific business requirements is vital. These needs range from authoring tools, federating data from various and dissimilar databases, and triggering processes and workflows. Download Now
White Paper - Industry 4.0 and the Future of Engineering Education
With industries becoming more automated, more tech-driven and more complex, engineers need to keep their skills and knowledge up to date in order to stay on top of this wave—and to be prepared for the Industry 4.0 future. The University of Cincinnati offers two online Master of Engineering degree programs designed specifically for practicing engineers. Download Now
White Paper - Comparing Multi-Patterning at 5nm: SADP, SAQP, and SALELE
Self-aligned multi-patterning techniques such as SADP, SAQP, and SALELE are increasingly popular at advanced nodes, but each process has its pros and cons. IMEC and Mentor, a Siemens business collaborated to identify potentially less-obvious process and design limitations and trade-offs between the three SAMP techniques. Learn more in this paper. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close