Jimmyg69
Industrial
- Mar 28, 2019
- 2
Hi all, I have a PSE PAR-70 Flow Sensor installed in the 1980's. What I need is to verify that the pressure transmitter and SCADA are scaled correctly. I have found a manual with the flow vs DP calculations in it but I'm having trouble with the math. I've attached a pic of the page from the manual. The pipe ID is 54", The fluid is water with a specific gravity of .998 and the flow rate quantity is US Gallons per minute. Currently the pressure transmitter is scaled at 0-33.7 inches of water and the SCADA is scaled 0-80 MGD (55,555.56 GPM). I calculate that 33.7 inches of water = 85.1 MGD (59097 GPM). I would appreciate any help. Thank You.