Bolt/threaded rod strengths differ for Grade 8.8 in BS 4190 and BS 5950

Bolt/threaded rod strengths differ for Grade 8.8 in BS 4190 and BS 5950

Bolt/threaded rod strengths differ for Grade 8.8 in BS 4190 and BS 5950

(OP)
BS 4190 says the bolt/thread rod strength for Grade 8.8 is 640 MPa. BS 5950 says it's 560 MPa for the same material. Why the difference? There is no difference for Grade 4.6, but there is again a difference for Grade 10.9. Thanks.

RE: Bolt/threaded rod strengths differ for Grade 8.8 in BS 4190 and BS 5950

is BS 5950 still valid ??

RE: Bolt/threaded rod strengths differ for Grade 8.8 in BS 4190 and BS 5950

(OP)
There are certain areas where the superseded codes may still need to be used, such as in the assessment of existing buildings. However, this is just something I had noticed and it's been bugging me. If anybody had come across this before and know of the reason, your help in answering the question above is appreciated.

RE: Bolt/threaded rod strengths differ for Grade 8.8 in BS 4190 and BS 5950

Not sure about the reason but the reason but the ISO 898 says Rp0,2 for 8.8 is 640 MPa and Rm = 800 MPa

RE: Bolt/threaded rod strengths differ for Grade 8.8 in BS 4190 and BS 5950

What do the mill test certificates (if available) say?
If you're checking an existing structure, I'd be inclined to go with the lesser value. Otherwise, I see no reason not to use 80% of 800 MPa, as that's the whole idea of the denomination of the fasteners.

RE: Bolt/threaded rod strengths differ for Grade 8.8 in BS 4190 and BS 5950

Hello P.J.
i don't have that BS under my hand, nevertheless the effect is known from similar standards.
640 Mpa is the materials nominal yield strength (8x8* 10).
560 MPa is the permitted stress of that material under tension load.
The bolt shall not be tensioned to full yield strength, but instead to a lower value which then still allows for operational loads.
Pls. refer explanatory notes, for
- pretensioning
- allowed loading when thread is in shear plane / not in s. p.
- combined loading (tension and shear)
There's some threads on EngTips on this one, too.
Regards

Roland Heilmann

RE: Bolt/threaded rod strengths differ for Grade 8.8 in BS 4190 and BS 5950

(OP)
Thanks Roland. That's an explanation I can accept.

Although there is no such difference for the Grade 4.6 bolt, I can accept that for such weaker bolts, the design strength (or allowable strength) for the Grade 4.6 bolt is very close to its material strength, such that the two codes had used a common value.

Also note that the description in BS 4190 is "Strength grade designations for steel bolts and screws", while that for BS 5950 is "Tensile strength of bolts". This difference matches your explanation for the discrepancy.

RE: Bolt/threaded rod strengths differ for Grade 8.8 in BS 4190 and BS 5950

I thought about this and come up with this. I could install 2 anchor bolts, on the 8" vertical leg, shim up the 4" leg with shim plates. Then the contractor could inject epoxy grout or suitable grout under the 4" leg to fill the gaps. Those 2 rows of anchor bolts on the side would be able to hold the angle up, with the shim plates and the grout under the 4" leg. It should be sufficient to hold things up.

The application is to prevent further concrete spalling on the vertical edge of a wall supporting precast panels over a road crossing. If you have a better suggestion, let's hear them. Thank you guys for the feedback.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close