Resort Hotel fire protection requirements in Asia

Resort Hotel fire protection requirements in Asia

Resort Hotel fire protection requirements in Asia

(OP)
Hi friends little off topic but important for me.
We have project - hotel resort type in Sri Lanka, 75 rooms separated to 2 storeys buildings per 4 rooms each with area of footprint 140 m2 each allocated within 20 m from each other.
Local fire department issued requirements to make :

Hose reel System 11*19 mm* 30 m hose reel providing 30 l/m with 6 m throw
and

Fire Hydrant System
Pillar type hydrants 02*65 mm capable to maintain minimum of 300 kpa residual pressure at the 10 l/s whyle two hydrants are operating.

We can ask to reduce requirements to only Hose reel system as hydrants with given capacity very expensive and probably fire department let us do it as the other hotels done it before but is it actually safe to have only hose reel systems without hydrants in such kind of objects?

RE: Resort Hotel fire protection requirements in Asia

So how is the fire department going to get the water supply for their fire engines if you replace the hydrants with hose reels.

RE: Resort Hotel fire protection requirements in Asia

(OP)
The resort is mostly with pedestrian type paths, they will be unable to drive to hydrants anyway.
As far as I understand they going to manually operate the hydrants.

RE: Resort Hotel fire protection requirements in Asia

Fire engines have segmented 2-1/2" fire hoses which they can assemble and connect to the nearest hydrants as The fire engines have their own pumps to supply the flow needed to extinguish fires. Hose reels are too small in diameter to provide the necessary flow rates regardless of the water pressure available.

RE: Resort Hotel fire protection requirements in Asia

Oops! hose connection between truck and fire hydrant is greater that 2-1/2"and if my recollection is somewhat correct is 6" whereas hose size from trucks are 2-1/2".

RE: Resort Hotel fire protection requirements in Asia

In the USA supply hose (fire hydrant to fire engine)

2.5”; 3”, 4”, and 5” most modern FD will use 4” or 5”

RE: Resort Hotel fire protection requirements in Asia

(OP)
Thanks guys!
I will try to specify my issue - due to remote location of the resort, I understand the fire service want us to be able fight fire before arriving of fire vehicle with fire engines. We dont have community water supply, we have deep well, RO plant and water tanks and designing our in house water supply systems with pump sets.
We also need to make separate or combined fire fighting water supply lines and pumps as per requirements.

They asked us to have system capable to operate two hydrants the same time, each flow 10 l/s - our fire pumps have to provide this capacity. It will give us totally 20 l/s that it seems to be too much for resort populated with 150-300 people. We can try to convince them to reduce requirements of maintaining flow to 10 l/s but the question is - if it officially safe to have system with capacity 10 l/s or less for this kind of object?

RE: Resort Hotel fire protection requirements in Asia

Install a fire sprinkler system in all buildings to NFPA 13 requirements!!!

Than maybe look at reducing flow

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper - PLM and ERP: Their Respective Roles in Modern Manufacturing
Leading manufacturers are aligning their people, processes, and tools from initial product ideation through to field service. They do so by providing access to product and enterprise data in the context of each person’s domain expertise. However, it can be complicated and costly to unite engineering with the factory and supply chain. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close